MikhailModeratorThe values in the table, also black, not red and green. This means that input channels are not configured properly. You should also set the Unit field to Off-On.
MikhailModeratorPlease contact us by email for more info.
MikhailModeratorCreate a table view to check color of values.
MikhailModeratorSorry, I mean:
Open Line 2 Parameters – Request Sequence, select the device 1 and then make a screenshot.
MikhailModeratorHello,
It’s possible to deploy a virtual machine in the cloud (Google, Azure, AWS, etc.) and install Rapid SCADA on that machine.
For our servers we use different providers. You should select your favorite.
MikhailModeratorDid you upload the project after change?
Create a table view to check color of values.
MikhailModeratorHi,
You need Automatic Control Module for this purpose.
MikhailModeratorChange channel type to Discrete
MikhailModeratorTimeout can be only be set to ‘System.Threading.Timeout.Infinite’ or a value > 0.
Please make a screenshot of the device properties in Communicator.
MikhailModeratorScreenshots would clarify the situation.
MikhailModeratorHi,
Please make screenshots of the input channels and the toggle properties.
MikhailModeratorError establishing TCP connection: No connection could be made because the target machine actively refused it 172.27.1.210:502
This message means that the PLC is not available by the IP 172.27.1.210 and port 502.
You should check the PLC.
MikhailModeratorHello,
Please provide a part of communication line log.
MikhailModeratorIncrease a delay or a period in the device properties (Communicator settings, communication line parameters, request sequence).
MikhailModeratorI confirm also work with latest version of
Great! Could you summarize what a user should do if he faces such problem?
-