MikhailModeratorIf you use GSM modems, you can try a mode when Communicator is TCP server, and a modem is TCP client, so a modem doesn’t need static IP address.
MikhailModeratorHi,
1. Press Ctrl+F5 in browser to update cached scripts.
2. Check if C:\SCADA\ScadaWeb\config\PlgChartPro.xml exists. This file also must be included in the project.
MikhailModeratorHi,
Check the following:
1. Stop the server service.
2. Open current data and check value of the channel 1311. Use Administrator to view raw data. Does it correct?
3. Start server. Check value of the channel 1311 again. What is the value and status?
4. If it was reset, publish ScadaServer.log.Provide some screenshots.
-
This reply was modified 5 years, 5 months ago by
Mikhail.
MikhailModeratorThis bug is really strange. You are the first who faced it. Could you provide some screenshots to show the sequence of steps before the problem?
MikhailModeratorWe can continue if you provide screenshots.
MikhailModeratorBefore checking Auto Control Module, we need to know what channel values and statuses are really calculated.
MikhailModeratorOpen data files remotely is not a good solution, because they might be too big. I think we should add a web viewer that displays raw data.
MikhailModeratorSince I can’t open the any log under Server/Archive/ from RSAdmin
If you mean current or historical data, use ScadaDataTest utility.
MikhailModeratorSince I can’t open the any log under Server/Archive/ from RSAdmin
You can open logs from text files in any time.
After sending a new value using Generator, check the actual channel data
Administrator – Instances – Default – Server – Archive – Current DataIf the channel data differs from the expected, let me know what channel data was expected and what is the actual result.
MikhailModerator5.7.1 is too old. I suggest to install v5.8.2 that includes Administrator 5.5.2.1.
MikhailModeratorI could not find any way to easily determine which version of Rapid SCADA is installed.
Rapid SCADA contains many applications. A user can upgrade them separately. The easiest way is to keep the downloaded installation package.
MikhailModeratorModbus does not support historical data. Only if a manufacturer deviated from the standard.
MikhailModeratorHi,
To download historical data from controllers:
1. A controller have to support this feature.
2. A new Rapid SCADA driver should be developed to implement the communication protocol of the controller.To discuss in Russian, use https://forum.rapidscada.ru/
MikhailModeratorI did the above and got the following in ModAutoControl.log
2020-12-30 10:37:47 Trigger state changed "ENV\F0-LAN/WAN-A": Waiting 2020-12-30 10:37:55 Trigger state changed "ENV\F0-Komora-A": Waiting 2020-12-30 10:38:31 Trigger state changed "ENV\F0-Komora-A": Firing 2020-12-30 10:38:31 Command is enqueued to be sent at 10:38:31. Device 1000, Command 1 2020-12-30 10:38:31 Sending trigger commands completed 2020-12-30 10:38:31 Command is sent. Device 1000, Command 1
Try the same and tell about results.
Note: I don’t recommend to use Averaging checkbox of input channels because it is deprecated and will be removed. Use the formulas instead.
MikhailModeratorWhich particular log is not displayed with the error message? Please provide links to screenshots.
-
This reply was modified 5 years, 5 months ago by
-