MikhailModeratorHi,
Yes, you can use archive replication for this purpose.
Command example for database exportcmd=ExportArchive startDT=2022-12-23 10:00:00 endDT=2022-12-23 11:00:00
MikhailModeratorNote that the above works in Rapid SCADA 6.
MikhailModerator🙂
MikhailModeratorAccording to the log, TCP server is waiting for incoming connections, but no client is trying to connect.
Is Rapid SCADA installed on a cloud server or in the local network?
MikhailModeratorMake sure that you copied PlgChartPro.xml and PlgChartPro_Config.xml into the project.
MikhailModeratorAlso try to connect to Communicator by any TCP client utility. You should see that a connection is established.
MikhailModeratorHello Ibrahim,
Please provide screenshots of the Communicator settings and the communication line log.
Make sure that the modems are configured to initiate a connection to the TCP server.
MikhailModeratorI recommend to upgrade Rapid SCADA to the latest version.
MikhailModeratorThank you.
MikhailModeratorDevice status is available. Each device in Communicator contains a hidden tag with the code
Status
If you create a channel, specify the device and tag code (Status), the device status will be received in this channel. 0 – normal, 1 – errorLine status currently cannot be received by a channel. To implement this, there should be a channel number in the line options. But it looks ugly. We should find a better idea.
MikhailModeratorHi,
Saving data every minutes generates 1440 slices per day.
So, there are 1440 * 850 * 2688 = 3 290 112 000 data points.
Therefore the archive size is big.
MikhailModeratorCould you share the final settings? It can be useful for other users.
MikhailModeratorHi,
How many slices in a day? How many days?
MikhailModeratorHi,
Create only 1 subscription, named Voltage (delete 2 others). The subscription should contain 3 sub items (3 lines).
MikhailModeratorHi,
You need subitems as Voltage L1, Voltage L2 and Voltage L3. And only 1 subscription, -