  • in reply to: Using Internal variables/channels #16678
    Mikhail
    Moderator

    ModDiffCalculator is discussed here. It’s free and useful.

    in reply to: Auto report module errors #16674
    Mikhail
    Moderator

    Everything look fine except Auto Report Module automatically export the Event Report even I didn’t activate it.

    It’s a bug. Will be fixed in the next version.

    in reply to: Auto report module errors #16673
    Mikhail
    Moderator

    Everything look fine except Auto Report Module automatically export the Event Report even I didn’t activate it.

    Restart the service after changing the configuration.

    in reply to: Auto report module errors #16671
    Mikhail
    Moderator

    Hi,

    After I change culture to en-GB, no errors at log and excel file (Historical Data Report & Elastic Report) when I opened them.

    The PlgElasticReport.zh-Hans.xml file includes a line
    <Phrase key="WorksheetName">工作表{0}</Phrase>
    Likely there is some forbidden character.
    Try replacing that line by the similar line from PlgElasticReport.en-GB.xml

    • This reply was modified 3 months ago by Mikhail.
    in reply to: Swapping command values #16670
    Mikhail
    Moderator

    In case of Modbus coils
    Cmd > 0 ? 0 : 1

    in reply to: Swapping command values #16669
    Mikhail
    Moderator

    Hi,
    In the output formula of the channel, put something like
    Cmd > 0 ? 0xFF : 0x00
    If it doesn’t work, make screenshots.

    in reply to: Using Internal variables/channels #16668
    Mikhail
    Moderator

    Hello,
    To do that, add a new function in the Scripts table, and then use it in a channel.

    public void MyFunc()
    {
      SetData(501, Val(500), 1);
      SetData(502, Val(501)-Val(500));
    }
    in reply to: Scada webstation not getting open #16667
    Mikhail
    Moderator

    can you link me with some example projects backup? I will try to restore the project and learn from there.

    The Hello World project is in C:\Program Files\SCADA\ProjectSamples\HelloWorld
    Other projects are owned by the customers.
    There is a YouTube video about connecting devices by Modbus. It should not be hard.

    in reply to: Using Internal variables/channels #16655
    Mikhail
    Moderator

    Hello,

    I have tried to make channels which aren’t linked to any device/communication lines

    I suggest to add a device in the Devices table that has no a real device under it. It is useful for grouping channels.

    SetData(417,Cmd,1)

    If that output formula is used in the channel 417 itself, it can be simplified to SetData()

    in reply to: Faster thread #16654
    Mikhail
    Moderator

    5000 channels is not so many. It should be 10 iterations per second. To measure it, you could write timestamps in a text file from a channel formula. A formula for writing to file somewhere on the forum.

    in reply to: Scada webstation not getting open #16653
    Mikhail
    Moderator

    Hi,
    What do you see in the modules window?
    Note that ASP.NET 8 must be installed after IIS.

    in reply to: Auto report module errors #16638
    Mikhail
    Moderator

    Hi,
    1. Could you make a screenshot of the report when you download the same report from a web page?
    2. What result do you get if you choose the HTML format in the Auto Report settings?
    3. Try using en-GB culture if you use another culture.

    in reply to: Faster thread #16637
    Mikhail
    Moderator

    Hello,

    This has led to a polling cycle of calculation taking up to 10 seconds.

    How did you calculate that?

    in reply to: Faster thread #16632
    Mikhail
    Moderator

    Hello,
    The main loop of the Server service iterates approximately 10 times a second. If you need faster calculation rate, I suggest to develop a specific module in C#.

    in reply to: Send Commond #16631
    Mikhail
    Moderator

    if I want to determine that the conditions of Channel1==1 && Channel2==2 are met, and I want to send the Value of Channel3

    It can be configured in Auto Control Module using a Multi-Channel Data Trigger.