Viewing 15 posts - 4,576 through 4,590 (of 6,299 total)
  • in reply to: Siemens Logo! Modbus #4483
    I ended up going to
    Please don’t mention other products on this forum.
    in reply to: OPC write value issue-IBH opc server #4472
    Try this dll.
    in reply to: Events trigger and colors #4471
    Also, is there a way of recording only one condition of the event?
    Currently no. Some modifications should be done to implement it.
    in reply to: Events trigger and colors #4470
    Event color depends on status color of the input channel. I mean you should change colors of Off-On values.
    Create your own record in the Units table, for example,
    Normal; Alarm; –
    And use formulas for setting the status of the input channel:
    Cnl; Cnl > 0 ? 114 : 13
    in reply to: Siemens Logo! Modbus #4468
    Hennie, you may try the above recommendations.
    in reply to: Create gauge, bar,… #4462
    Read this dialog about building the project.
    You should use the existing components as examples. Gauge and level components already available here.
    Here on the forum I can answer particular technical questions. Be free to ask. Detailed individual lessons are available for a fee.
    in reply to: OPC write value issue-IBH opc server #4460
    Thank you for the screenshots. I will send you a special version of the OPC driver and we can check again and compare info from OPC analyzer.
    in reply to: OPC write value issue-IBH opc server #4454
    I will send you a test version of KpOpc.dll during the week 22-28 of October.
    in reply to: Usage of the popup #4452
    Thank you for the information about the solution.
    in reply to: OPC write value issue-IBH opc server #4451
    Is it possible to write with IOPCSyncIO::Write?
    I don’t think that this is possible.
    In the source code of KpOpc.dll driver I just use daServer.Write(new Opc.Da.ItemValue[] { itemVal }); and the library made by OPC Foundation choose lo-level method WriteVQT.
    I can try setting Quality field of the item being written.
    in reply to: Reading bits #4445
    In communicator I can see that the register is just bound to one input channel but I want to give it to 16 input registers. How this is possible?
    One input channel is bound to only 1 tag in Communicator. For further calculations, you need to use one input channel (real type) as a source and other input channels of calculated type. If you post a link to a screenshot of your input channels, it would be easier to find a mistake.
    in reply to: OPC write value issue-IBH opc server #4444
    Try switch to OPC DA 2 in Communicator and check what write command is used.
    I can set Quality in the driver, but before I do it, it’s better to hear an answer from the OPC server developer.
    in reply to: Reading bits #4441
    Could you provide an example?
    Note: formulas are calculated in order of input channel numbers.
    in reply to: Usage of the popup #4440
    Hi Ben,
    Probably the old scripts are cached by a browser. Clear the browser cache or press Ctrl+F5 in a scheme web page.
    in reply to: Remote commumicator #4431
    If you use remote Communicator, you need the only one Communicator application on a remote PC. Other Rapid SCADA apps should not be installed there.
    In other case, if you have 2 Rapid SCADA servers, you can use Rapid Gate module to transfer data.