Viewing 15 posts - 4,066 through 4,080 (of 6,302 total)
  • in reply to: hide the plugins menu in the web #5864
    i hidden the plugins menu by code changed in scadaweb.
    What code did you change? Restore it back if needed.
    in reply to: More about DBExport. #5859
    It is possible to customize data sending to DB
    You can filter data by changing SQL queries in the module settings.
    Note: if you’d like, you can write to the Russian forum. It’s up to you.
    in reply to: More about DBExport. #5857
    What is the trigger of the exporting current data?
    When Communicator sends data to the Server app. It sends the values twice, because it does it after a communication session, and with fixed intervals.
    If you set “Period of sending all device tags” to 0 (in Communication – Common Parameters), you will avoid duplication.
    in reply to: Server Problem #5856
    You’ve provided the local link. Please provide a screenshot.
    in reply to: ASCII text #5846
    This is possible if you split the text into 2 parts. I know this is hard, but currently it works so.
    If you have limited number of phrases to display, use enumerations.
    in reply to: sending only zero command by communicator #5845
    Please try:
    BitConverter.ToDouble(new byte[] { 0x00, 0x00, 0x01, 0x00, 0x00, 0x00, 0x00, 0x00}, 0)
    I don’t test formulas on the forum, because this is a part of Extended Support.
    in reply to: User input through Scheme #5844
    As a recap of the above post, you need to create an input channel, an output channel, and use SetVal(…) for the output channel.
    If you provide screenshot of your configuration database, we can validate it.
    in reply to: Error message in scada server #5843
    In most cases SCADA-Server starts automatically and you don’t need to start it manually. Please watch our videos and do the same.
    How to translate this error?
    in reply to: sending only zero command by communicator #5830
    If you send Standard command you can play with a formula of input channel:
    BitConverter.ToDouble(new byte[] { 0x00, 0x00, 0x01, 0x00, 0x00, 0x00, 0x00, 0x00})
    In the formula set the required byte to 1.
    in reply to: sending only zero command by communicator #5829
    To assign multiple coils, you should send a command of binary type and specify a byte array as a command data.
    The command data array contains 00 and 01 as I remember.
    in reply to: Writing output coil registers #5828
    If a device provide flags as uint, likely you need to set them as holding register by a function 06. Isn’t it?
    In case you need to mix functions 05 and 06 that is out of Modbus standard, you should modify the driver source code.
    in reply to: Modbus Serial Config #5827
    it takes me to device “x” stats for example Email, OPC instead of for the actual device.
    Likely log files was not updated. After you upload configuration, check status of the Server and Communicator applications.
    is float32 available as config for communicator decode of data?
    If you ask about Modbus, yes.
    in reply to: Writing output coil registers #5822
    I would like to send the command with function code – 05 and want to declare the register as 02 bytes uint.
    According to the Modbus specification, function 05 is used to set a coil. Coil is a one bit, so you can’t set uint by function 05.
    To set holding registers, function 06 is used.
    in reply to: Send Modbus Signal to other SCADA #5821
    Option 1. Via external database as manjey73 said. See this link.
    Option 2. We can develop OPC UA server or Modbus Slave driver for Rapid SCADA by a custom contract.
    in reply to: Writing output coil registers #5817
    It’s a good idea to create a one command while testing.
    To set 2 bytes register, choose Holding Registers in command properties.
    Watch the new video about it.