  • Mikhail
    There is no software limits. However, if you have many connections, you should test if the network is good enough for that.
    in reply to: V6 ModDbExport for historical data #14541
    Yes, you can use archive replication for this purpose.
    Command example for database export
    cmd=ExportArchive
    startDT=2022-12-23 10:00:00
    endDT=2022-12-23 11:00:00
    in reply to: Modbus Data Formula #14539
    Note that the above works in Rapid SCADA 6.
    in reply to: Chart not Displaying Data #14528
    in reply to: Modbus TCP Server #14526
    According to the log, TCP server is waiting for incoming connections, but no client is trying to connect.
    Is Rapid SCADA installed on a cloud server or in the local network?
    in reply to: Chart not Displaying Data #14521
    Make sure that you copied PlgChartPro.xml and PlgChartPro_Config.xml into the project.
    in reply to: Modbus TCP Server #14520
    Also try to connect to Communicator by any TCP client utility. You should see that a connection is established.
    in reply to: Modbus TCP Server #14519
    Hello Ibrahim,
    Please provide screenshots of the Communicator settings and the communication line log.
    Make sure that the modems are configured to initiate a connection to the TCP server.
    in reply to: Chart not Displaying Data #14516
    I recommend to upgrade Rapid SCADA to the latest version.
    in reply to: How to extract MQTT message completely #14513
    Device status is available. Each device in Communicator contains a hidden tag with the code Status
    If you create a channel, specify the device and tag code (Status), the device status will be received in this channel. 0 – normal, 1 – error
    Line status currently cannot be received by a channel. To implement this, there should be a channel number in the line options. But it looks ugly. We should find a better idea.
    in reply to: RapidGate #14509
    Saving data every minutes generates 1440 slices per day.
    So, there are 1440 * 850 * 2688 = 3 290 112 000 data points.
    Therefore the archive size is big.
    in reply to: How to extract MQTT message completely #14508
    Could you share the final settings? It can be useful for other users.
    in reply to: RapidGate #14504
    How many slices in a day? How many days?
    in reply to: How to extract MQTT message completely #14503
    Create only 1 subscription, named Voltage (delete 2 others). The subscription should contain 3 sub items (3 lines).