Viewing 15 posts - 1,021 through 1,035 (of 6,219 total)
  • in reply to: OPC UA client connection setup ? #14583
    Note that you can write some info to a text file from script to debug your formula.
    in reply to: OPC UA client connection setup ? #14582
    The idea of the formula is below.
    String are encoded in Unicode, split into byte arrays and save into channels that have Double data type.
    In a formula you need to convert Doubles back into strings. Then join, and convert from string to double.
    If a channel has length > 1, the Server internally creates several channels with sequent numbers, so you can access their data as usual.
    In the Script table, find the [5] Strings functions. They will be useful for your purpose.
    in reply to: OPCUA Remote Configuration Issue #14581
    The other possible approach we use in DrvOpcClassic.
    A user can download the structure of the OPC tags to an XML file using a utility. Then open that XML file by a driver UI instead of connecting to an OPC server. May be this approach is straightforward and easy for understanding.
    For example, a customer can send you an XML file containing OPC nodes. Then an engineer can use it in his office.
    in reply to: OPC UA View in ScadaAdmin can’t connect in Wine 9.8 #14580
    OK, let’s continue in this thread.
    in reply to: E mail #14579
    As far as I know, you can’t send emails via Gmail by 3rd party apps anymore. You should use another mail server.
    https://yandex.com/ should work for now. Or use your local mail providers.
    in reply to: Where is Administration Application #14578
    Note: It’s possible to run the Administrator app using Wine 9.x on Linux. But it’s not so easy. I suggest to use it on Windows.
    in reply to: rapidscada 6.1 install on linux problem #14577
    Download ScadaAdmin for Linux. Works on Wine. Note that it is easier to use the Administrator app on Windows.
    in reply to: SMS #14566
    SMS can be sent by different methods: via GSM modem and HTTP service (country dependent).
    What method do you prefer?
    in reply to: OPC UA View in ScadaAdmin can’t connect in Wine 9.8 #14565
    This is probably your pull request? Does i solve the issue?
    in reply to: Error uploading configuration #14564
    Thank you for the info.
    Probably, the issue was caused by .NET installation problem.
    in reply to: Where is Administration Application #14563
    In addition, this video shows how to connect from the Administrator app, which is installed on Windows, to a Linux instance of Rapid SCADA.
    in reply to: OPC UA client connection setup ? #14562
    That article is about configuring OPC Classic for Rapid SCADA 5.
    > What about the timeout, delay, time, period, string address or host name, name ?
    Time and period do not work. Address is ignored. Delay is used internally. I recommend to use the default values.
    > Also on the TagName thing, for the first time, I need to join two OPCUA string values together.
    It would be easier if you get a string in a one OPC UA tag instead of joining channels. Concatenation of string channels is possible, but the formula may be tricky.
    in reply to: Comparing two values with using formula #14545
    You need to add a new channel of the calculated type with a formula
    Val(101) > Val(102) ? 1 : 0
    where 101 and 102 the channels to compare.
    Then use Automatic Control Module to send command according to the value of the added channel.
    If you have questions during the implementation of the above solution, send screenshots of your settings.
    You don’t need to disable firewall. You need to configure it. Allow incoming connections to the TCP port in use.
    Please use different topics for different questions. Discussion about scheme components should be in other thread.
    There is no software limits. However, if you have many connections, you should test if the network is good enough for that.
