Marko
Viewing 15 posts - 1 through 15 (of 38 total)
  • in reply to: Automatic Control Module – Registration key invalid #17229
    Marko
    Dear Mikhail,
    sorry for late response. I did update project once again and miraculously it is start working again. Key is valid. Really don’t know what happen. I will note you if I encounter this problem again. Thank you.
    in reply to: User options #14502
    Marko
    Thank you for the info.
    in reply to: Server problem #7584
    Marko
    Hello Mikhail,
    just to note that server is stable and wanted to thank you for your support.
    in reply to: Server problem #7450
    Marko
    Hello Mikhail,
    I did change triggers how you mention and server is stable for now. It is working like that for 5 days. I will test it a little bit more and keep you noted.
    in reply to: Server problem #7431
    Marko
    The properties of channel 653 and 753 is the same. So i will show you only channel 653.
    Here is link about automatic module setup of channel 653:
    https://imgur.com/kMkCVfx
    Here is link about setup of output channel 653:
    https://imgur.com/zwimPcL
    Here is link of formula that channel 653 is using:
    https://imgur.com/URjPCce
    Just to inform you a little better. We using formula to get minute from server time and send it to remote location. It’s like watchdog for remote locations to know when server is down from some reason. Furthermore remote locations send email that server or scada is down. This information is important for us because it’s only way we can detect problems with server or scada automatically.
    in reply to: Server problem #7421
    Marko
    i manage to get information from communicator log when server stop.
    2020-10-12 16:36:31 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-12 16:37:11 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-12 16:37:31 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-12 16:38:11 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-12 16:38:31 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-12 16:39:11 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-12 16:39:31 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-12 16:40:11 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-12 16:40:42 <VMI398773><SYSTEM><EXC> Error sending current data to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-12 16:40:42 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-12 16:40:42 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-12 16:40:47 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-12 16:40:47 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-12 16:40:47 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-12 16:40:48 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    Last command that was sent was from device 61 as you see in log. That is channel 653.
    in reply to: Server problem #7419
    Marko
    Hello Mikhail,
    from comunicator logs early as i can get after server problem was this:
    2020-10-11 00:16:12 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-11 00:16:17 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-11 00:16:17 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    Server was down from 00-14 until 00-54.
    Also i do not have data in archive when server was down in that period of time.
    in reply to: Server problem #7401
    Marko
    What was the first timestamp when Communicator couldn’t connect?
    I am not able to find first timestamp because log is full in 2 hours. I will send if i get error before 2 hours of occuring.
    This is feeling log pretty quickly
    2020-10-08 07:17:50 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-08 07:17:51 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-08 07:17:52 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    in reply to: Server problem #7400
    Marko
    Try to change the command settings in the trigger:
    – Set “Out channel” to 0
    – Set “Device” to non-zero instead of output channel.
    That will work if you don’t use a formula of the output channel 653.
    I am using formula in channel 653 and 753.
    Automatic control module version is 5.2.5.0
    in reply to: Server problem #7388
    Marko
    1. I have commands that i sanding every minute to some devices.
    2.I can’t find that first timestamp because in mean time log has changed completely.
    I did get problem again this morning and i found this:
    2020-10-07 07:35:03 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:35:04 <VMI398773><SYSTEM><ACT> Stop communication lines
    2020-10-07 07:35:04 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: A request to send or receive data was disallowed because the socket is not connected and (when sending on a datagram socket using a sendto call) no address was supplied
    2020-10-07 07:35:04 <VMI398773><SYSTEM><EXC> Error restoring connection with SCADA-Server: Thread was being aborted.
    2020-10-07 07:35:04 <VMI398773><SYSTEM><EXC> Error requesting telecommand from SCADA-Server: Thread was being aborted.
    2020-10-07 07:35:04 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:35:04 <VMI398773><SYSTEM><ACT> Receiving commands aborted
    2020-10-07 07:35:09 <VMI398773><SYSTEM><ACT> ScadaCommService is stopped
    2020-10-07 07:35:09 <VMI398773><SYSTEM><ACT> ScadaCommService 5.2.1.0 is started
    2020-10-07 07:35:09 <VMI398773><SYSTEM><ACT> Load device library: KpEmail.dll
    2020-10-07 07:35:09 <VMI398773><SYSTEM><ACT> Load device library: KpModbus.dll
    2020-10-07 07:35:09 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:35:10 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: No connection could be made because the target machine actively refused it 127.0.0.1:10000
    2020-10-07 07:35:10 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:35:10 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    Delay before trying again
    2020-10-07 07:35:21 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:35:22 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: No connection could be made because the target machine actively refused it 127.0.0.1:10000
    2020-10-07 07:35:22 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:35:22 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:35:32 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:35:37 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:35:37 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:35:37 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:35:47 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:35:53 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:35:53 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:35:53 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:36:03 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:36:09 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:36:09 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:36:09 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:36:19 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:36:24 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:36:24 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:36:24 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:36:34 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:36:40 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:36:40 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:36:40 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:36:50 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:36:55 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:36:55 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:36:55 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:37:06 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:37:11 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:37:11 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:37:11 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:37:20 <VMI398773><SYSTEM><ACT> ScadaCommService is stopped
    2020-10-07 07:37:23 <VMI398773><SYSTEM><ACT> ScadaCommService 5.2.1.0 is started
    2020-10-07 07:37:23 <VMI398773><SYSTEM><ACT> Load device library: KpEmail.dll
    2020-10-07 07:37:23 <VMI398773><SYSTEM><ACT> Load device library: KpModbus.dll
    2020-10-07 07:37:23 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:37:28 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:37:28 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:37:28 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:37:39 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:37:41 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: An existing connection was forcibly closed by the remote host.
    2020-10-07 07:37:41 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:37:41 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:37:52 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:37:58 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:37:58 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:37:58 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:38:08 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:38:13 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:38:13 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:38:13 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:38:23 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:38:29 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:38:29 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:38:29 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:38:39 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:38:44 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:38:44 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:38:44 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:38:55 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:39:00 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:39:00 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:39:00 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:39:10 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:39:16 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:39:16 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:39:16 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:39:26 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:39:31 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:39:31 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:39:31 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:39:42 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:39:47 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:39:47 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:39:47 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:39:57 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:40:03 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:40:03 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:40:03 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:40:13 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:40:18 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:40:18 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:40:18 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:40:28 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:40:34 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:40:34 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:40:34 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:40:44 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:40:50 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:40:50 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:40:50 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:41:00 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:41:05 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:41:05 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:41:05 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:41:15 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:41:21 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:41:21 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:41:21 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:41:31 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:41:36 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: Unable to read data from the transport connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond.
    2020-10-07 07:41:36 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-07 07:41:36 <VMI398773><SYSTEM><ERR> Unable to start operation due to SCADA-Server communication error.
    2020-10-07 07:41:41 <VMI398773><SYSTEM><ACT> ScadaCommService is shutdown
    2020-10-07 07:42:27 <VMI398773><SYSTEM><ACT> ScadaCommService 5.2.1.0 is started
    2020-10-07 07:42:27 <VMI398773><SYSTEM><ACT> Load device library: KpEmail.dll
    2020-10-07 07:42:27 <VMI398773><SYSTEM><ACT> Load device library: KpModbus.dll
    2020-10-07 07:42:28 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-07 07:42:29 <VMI398773><SYSTEM><ACT> Start communication lines
    2020-10-07 07:42:29 <VMI398773><SYSTEM><ACT> Start receiving commands
    2020-10-07 07:42:31 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-07 07:42:32 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-07 07:42:33 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-07 07:42:34 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    We made shortcuts for restart scada server and communicator and after restart of both scada was still shutdown. We then did restart of PC and Scada started to work again.
    3. I don’t know how to check version of automatic control module.
    4. Screenshot of command:https://imgur.com/3suaPM6
    5. Those commands from picture i changed to repeat only once. So in this case they are sending only 2 commands per minute. Channel 653 and 753 once every minute.
    in reply to: Server problem #7370
    Marko
    SCADA – Server version is 5.1.3.0.
    SCADA Server logs around time when application closed
    2020-10-05 23:11:35 <VMI398773><SYSTEM><ACT> Command: out channel = 753, user ID = 0
    2020-10-05 23:12:11 <VMI398773><SYSTEM><ACT> Command: out channel = 653, user ID = 0
    2020-10-05 23:12:12 <VMI398773><SYSTEM><ACT> Command: out channel = 653, user ID = 0
    2020-10-05 23:12:13 <VMI398773><SYSTEM><ACT> Command: out channel = 653, user ID = 0
    2020-10-05 23:12:14 <VMI398773><SYSTEM><ACT> Command: out channel = 653, user ID = 0
    2020-10-05 23:12:15 <VMI398773><SYSTEM><ACT> Command: out channel = 653, user ID = 0
    2020-10-05 23:12:31 <VMI398773><SYSTEM><ACT> Command: out channel = 753, user ID = 0
    2020-10-05 23:12:32 <VMI398773><SYSTEM><ACT> Command: out channel = 753, user ID = 0
    2020-10-05 23:12:33 <VMI398773><SYSTEM><ACT> Command: out channel = 753, user ID = 0
    2020-10-06 00:29:26 <VMI398773><SYSTEM><EXC> Error processing new current data:
    System.Threading.ThreadAbortException: Thread was being aborted.
    at System.Threading.Monitor.Enter(Object obj)
    at Scada.Server.Engine.MainLogic.RaiseOnCurDataProcessed(Int32[] cnlNums, Srez curSrez)
    at Scada.Server.Engine.MainLogic.ProcCurData(Srez receivedSrez)
    2020-10-06 00:29:26 <VMI398773><SYSTEM><EXC> Error receiving and processing data from the client 127.0.0.1: Thread was being aborted.
    2020-10-06 00:29:26 <VMI398773><SYSTEM><EXC> Error communicating with the client 127.0.0.1: Thread was being aborted.
    2020-10-06 00:29:26 <VMI398773><SYSTEM><ACT> Connection listener is stopped
    2020-10-06 00:29:36 <VMI398773><SYSTEM><EXC> Error executing actions on current data calculated in module ModAutoControl: Thread was being aborted.
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Server is aborted
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> ScadaServerService is stopped
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> ScadaServerService 5.1.3.0 is started
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Module is loaded from the file C:\SCADA\ScadaServer\Mod\ModAutoControl.dll
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Check the existence of the data directories is completed successfully
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Check the existence of the configuration database files is completed successfully
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Input channels are read from the configuration database. Active channel count: 210
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Ouput channels are read from the configuration database
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Users are read from the configuration database
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Formulas are read from the configuration database
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> The formulas source code has been compiled
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Connection listener is started
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Start server
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Command: out channel = 753, user ID = 0
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Command is canceled
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ACT> Current data are loaded
    2020-10-06 00:29:37 <VMI398773><SYSTEM><ACT> Connect to client 127.0.0.1
    2020-10-06 00:29:37 <VMI398773><SYSTEM><ACT> The user ScadaWeb is successfully authenticated
    2020-10-06 00:29:37 <VMI398773><SYSTEM><ACT> The user ScadaComm is successfully authenticated
    2020-10-06 00:29:37 <VMI398773><SYSTEM><ACT> Check username and password for admin. Result: passed
    2020-10-06 00:29:37 <VMI398773><SYSTEM><ACT> Command: out channel = 753, user ID = 0
    2020-10-06 00:30:11 <VMI398773><SYSTEM><ACT> Command: out channel = 653, user ID = 0
    2020-10-06 00:30:12 <VMI398773><SYSTEM><ACT> Command: out channel = 653, user ID = 0
    2020-10-06 00:30:13 <VMI398773><SYSTEM><ACT> Command: out channel = 653, user ID = 0
    In 00:29 i did restart to scada-server. After that scada start working again. Command out channels should work every minute but after 23:12 they stopped until i did restart of scada.
    Communicator log around time when application closed
    2020-10-06 00:29:16 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:17 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:17 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-06 00:29:18 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: No connection could be made because the target machine actively refused it 127.0.0.1:10000
    2020-10-06 00:29:18 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-06 00:29:18 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:19 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:20 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:21 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:22 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:23 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:24 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:25 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:26 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:27 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:27 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-06 00:29:28 <VMI398773><SYSTEM><EXC> Error connecting to SCADA-Server: No connection could be made because the target machine actively refused it 127.0.0.1:10000
    2020-10-06 00:29:28 <VMI398773><SYSTEM><ACT> Disconnect from SCADA-Server
    2020-10-06 00:29:28 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:29 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:30 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:31 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:32 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:33 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:34 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:35 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:36 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:37 <VMI398773><SYSTEM><ERR> Unable to connect to SCADA-Server. Try again.
    2020-10-06 00:29:37 <VMI398773><SYSTEM><ACT> Connect to SCADA-Server “localhost”
    2020-10-06 00:29:37 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-06 00:30:11 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-06 00:30:12 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-06 00:30:13 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-06 00:30:14 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-06 00:30:15 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-06 00:30:31 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-06 00:30:32 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-06 00:30:33 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-06 00:30:34 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-06 00:30:35 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-06 00:31:11 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-06 00:31:12 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-06 00:31:13 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-06 00:31:14 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-06 00:31:15 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=61, number=4
    2020-10-06 00:31:31 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-06 00:31:32 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-06 00:31:33 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    2020-10-06 00:31:34 <VMI398773><SYSTEM><ACT> The command is received from SCADA-Server: type=Standard, device=62, number=4
    in reply to: Restart Scada #7297
    Marko
    in reply to: Can’t activate ChartPro plugin #6880
    Marko
    Thank you, i did activate it. In security i give modify permission to User account.
    in reply to: Modbus TCP – can't read device #6014
    Marko
    Remote software is not turn on 100% of time. We use software only to check is device working properly. The problem with connection occurs when remote software wasn’t active at all. There must be something else that result problem.
    in reply to: Download or upload configuration #5959
    Marko
    Hello Mikhail,
    i want to apologize for late response but i talked with my boss and he will contact you about details for method 1.