November 23, 2026 at 12:24 pm #18600
MSander68
ParticipantHello,
We are evaluating with redundancy as a hard requirement Modbus only TCP. I have read the existing redundancy thread, the Software Architecture page and the Rapid Gate Module documentation. As I understand it, Rapid Gate synchronizes current data, historical data, events and commands between a primary and a backup Server, but I could not find how switchover is meant to work.
Could you clarify the following?
Failover: Is there any built-in failover in v6? Can Communicator and Webstation be configured with a backup Server connection and switch automatically?
Or is switchover expected to be handled outside Rapid SCADA (virtual IP, DNS, manual)?
Recommended architecture: For primary/backup, do you recommend two complete instances (Server + Communicator + Webstation on each computer, both Communicators polling), or one active Communicator feeding both Servers?
Rapid Gate in primary/backup mode:
Should gateways be configured in both directions (A→B and B→A)?
If both Communicators poll the devices, should current data still be forwarded, or only events, acknowledgements and archives?The v5 docs mention that forwarded values may have their formulas applied twice on the target. Does that still apply in v6?
Event acknowledgement: What is the recommended way to keep acknowledgements consistent on both servers?
Licensing: Is one Rapid Gate license needed per Server in a primary/backup pair?
A short answer, or a pointer to an example configuration, would be very helpful.
Thank you!
November 23, 2026 at 12:37 pm #18602
MikhailModeratorHello,
Based on this document:
In Modbus TCP is used, the most simple method is polling a device by the main and backup Rapid SCADA instances in parallel independently. But data in archives might be slightly different.
In addition, each instance can write a few copies of data. For example, write files and write to PostgreSQL database.If you need the archives to be synchronized, it is described by “Automatic Poll Switching” at page 4. Two software modules work together: Rapid Gate and Replication Helper. The last one is included in Rapid SCADA Enterprise. This combination is somewhat complex to set up. If you’d like to give it a try, I can send you an example.
November 23, 2026 at 12:47 pm #18603
MikhailModerator> Failover: Is there any built-in failover in v6? Can Communicator and Webstation be configured with a backup Server connection and switch automatically?
Communicator can send data to several servers. Automatic switching is implemented by using Rapid Gate and Replication Helper.> Or is switchover expected to be handled outside Rapid SCADA (virtual IP, DNS, manual)?
To backup the web application, a 3rd party balancer is used in some implementation.> Recommended architecture: For primary/backup, do you recommend two complete instances (Server + Communicator + Webstation on each computer, both Communicators polling), or one active Communicator feeding both Servers?
My favorite is 2 different intendent instances because is clear and simple. Each includes Server, Communicator and Webstation.> Rapid Gate in primary/backup mode:
Should gateways be configured in both directions (A→B and B→A)?
If both Communicators poll the devices, should current data still be forwarded, or only events, acknowledgements and archives?
If Rapid Gate is used to sync data, only one Communicator should work at a moment.> The v5 docs mention that forwarded values may have their formulas applied twice on the target. Does that still apply in v6?
In v6, it is solved by Rapid Gate options.> Event acknowledgement: What is the recommended way to keep acknowledgements consistent on both servers?
There is a server option to generate a special command when an event is ack’ed. Such commands are transferred by Rapid Gate to sync acks.> Licensing: Is one Rapid Gate license needed per Server in a primary/backup pair?
Rapid Gate is needed on the main server.
Replication Helper is needed on the main and backup server.As a recap, Rapid SCADA supports various redundancy options. In my view, you should choose the simplest option that meets your needs. Of course, if you require the most comprehensive solution, then go with that one.
-