  • in reply to: Communication with Multiple Devices #5618
    manjey73
    Participant

    We need to spread the devices on different physical lines of communication.

    in reply to: Unknown device tags #5616
    manjey73
    Participant

    Could you share the wireshark logs that you received by scanning the packets ? If anything, there is the Allen Bradley Protocol.

    in reply to: Unknown device tags #5598
    manjey73
    Participant

    You can check if this applies to Modbus using this link
    Rapid SCADA Modbus Parser
    However, you need to find the right start and end of the parcel in the TCP scanner

    in reply to: Unknown device tags #5593
    manjey73
    Participant

    There is a similar task, but AB Micrologix is used, according to the description PLC data support Modbus, but it is used or not unknown. You must put the port watcher on the exchange between the PLC and the HMI panel to read the traffic between them. But not the fact that it will help. Plus, try to connect to the PLC with Modbus scanners.
    Google Переводчик

    in reply to: Could you help to make correct logic. #5452
    manjey73
    Participant

    Tell me, why do you then need to input 1 ?

    in reply to: Automatic control with Raspberry Pi #5257
    manjey73
    Participant

    It is also necessary to transfer the configuration of the module settings. And also buy a license for the module on RaspberryPi

    in reply to: Rapid Gate #5167
    manjey73
    Participant

    If the server is one of the main, the Rapid Gate is not needed.

    If there are several servers plus one main server, then Rapid Gate is needed for each slave server and the corresponding number of licenses for each Rapid Gate is required.

    A large diagram is specified without Rapid Gate

    • This reply was modified 6 years, 6 months ago by manjey73.
    in reply to: Address Modbus RTU #5140
    manjey73
    Participant

    Command type – Binary ??????? may ba Standard

    And you need to pass 0 or 1 ?

    • This reply was modified 6 years, 7 months ago by manjey73.
    in reply to: TCP/IP or MQTT #5119
    manjey73
    Participant

    On the site your GSM modem can establish a connection via VPN channel ?

    in reply to: Save #5073
    manjey73
    Participant

    See Dat files in folders c:\SCADA\ArchiveDAT\

    The data can be viewed using the Server application

    in reply to: formula input #5008
    manjey73
    Participant

    Divide formulas into several channels. If the formula returns double, you can use one formula inside another.

    for example

    NOT(OR(Val(100), Val(101)))

    public double NOT(double val)
    {
        bool boolVal = val > 0;
        return Convert.ToDouble(!boolVal);
    }
    in reply to: formula input #4987
    manjey73
    Participant

    Logical And

    public double AND(double in1, double in2)
    {
    bool q = false;
    bool i1 = in1 > 0;
    bool i2 = in2 > 0;
    q = i1&&i2;
    return Convert.ToDouble(q);
    }

    in reply to: formula input #4983
    manjey73
    Participant

    Judging by the logic you want to get logical OR ?

    Add formula to formula table

    public double OR(double in1, double in2)
    {
    bool q = false;
    bool i1 = in1 > 0;
    bool i2 = in2 > 0;
    q = i1||i2;
    return Convert.ToDouble(q);
    }

    Use in channel OR(Val (n), Val(m))

    • This reply was modified 6 years, 7 months ago by manjey73.
    in reply to: Mobile client and Rapid SCADA #4829
    manjey73
    Participant

    1. to do this, you must have an external static IP address for your server (router)
    2. Perform the necessary router settings to access your services from outside

    If this is not possible, use third-party services such as TeamViewer and others

    Remote access is already a task of IT sphere, not Scada as such.

    For example I have a dedicated static IP address. I connect to my router VPN client and see the entire internal network as if I was connected inside the network via Wi-Fi and moreover, the IP address on my phones to determine the third-party services becomes the same as when connecting VPN traffic begins to pass through my home router. Sometimes it is useful for sites that require access settings from certain IP addresses and will ignore you if the addresses are carrier-based.

    • This reply was modified 6 years, 9 months ago by manjey73.
    • This reply was modified 6 years, 9 months ago by manjey73.
    in reply to: Error data fire system #4822
    manjey73
    Participant

    KpModbus_test

    Try this library. If your device does not respond due to zero ID, it should work. In the future, Mikhail promised to add an identifier change in the release version of the library.

    If so, this is the second device that does not accept a null request ID.

    Still you have the difference
    00 25 00 00 00 06 01 03 00 00 00 0A
    00 00 00 00 00 06 F6 03 00 00 00 05

    • This reply was modified 6 years, 9 months ago by manjey73.
    • This reply was modified 6 years, 9 months ago by manjey73.
    • This reply was modified 6 years, 9 months ago by manjey73.