MikhailModeratorThe architecture is OK.
The last image cannot be open.
MikhailModeratorIf I copy the faceplate into standalone mimic diagram it works well.
If the faceplate is embedded in another mimic the pictures shows only default image.As a recap:
– Mimic A,
– Mimic B is inserted into Mimic A using the Frame component,
– Faceplate works well when it is on Mimic A, but has issues when it is on Mimic B.Is the above correct?
MikhailModeratorHello,
What is the architecture of your solution?
MikhailModeratorHello,
Good questions, I would also be interested to hear about practical experience with DNP3.
Is the additional layer (DNP3 → OPC → Rapid SCADA) generally stable and reliable for continuous operation?
I suppose, it depends on the particular OPC server.
MikhailModeratorHi,
Are the images loaded from the external web URL? If so, it would be better to include them into the faceplate file.
MikhailModeratorCurrently, unit is displayed in a tooltip of each table item.
MikhailModeratorI’ve added the idea to the backlog.
MikhailModeratorMy faceplates contain several images that represent the status of the switches: on, off, and undefined
If it is not related to the frame issue, please create a new topic.
-
This reply was modified 1 month ago by
Mikhail.
MikhailModeratorPublished at https://rapidscada.net/store/Module/en/ExtDepMicrosoftSqlJP
Thank you.
MikhailModerator
MikhailModeratorHi,
When a frame uses another origin (localhost:5000) than the main website (localhost:10008) is is usually blocked by a web browser according to security reasons. Try using the same host and port for frames.
MikhailModeratorHi,
There is no such an option in a table view, unfortunately.
MikhailModeratorCould you clarify 0x7FFF and 0x7FFFFFFF are input values provided by the controller, or output values send to the controller. Maybe publish some screenshots.
MikhailModeratorInstead, the online Rapid SCADA Modbus Parser treats CRC bytes as big-endians which seam inexact.
According to the practice, the Modbus Parser calculates correctly 🙂
If you find a difference in CRC comparing to the real Modbus device, let us know.
MikhailModeratorHi,
Please provide additional information:
1. Screenshot of the mimic in the frame.
2. Screenshot of possible errors in the browser console (by F12). -