  • in reply to: Server problem #7399
    Mikhail
    Moderator

    Waiting for the module version.

    in reply to: Server problem #7397
    Mikhail
    Moderator

    Try to change the command settings in the trigger:
    – Set “Out channel” to 0
    – Set “Device” to non-zero instead of output channel.

    That will work if you don’t use a formula of the output channel 653.

    • This reply was modified 5 years, 3 months ago by Mikhail.
    in reply to: Server problem #7396
    Mikhail
    Moderator

    We made shortcuts for restart scada server and communicator and after restart of both scada was still shutdown

    Likely ScadaServerSvc.exe process should be killed in such case.

    I don’t know how to check version of automatic control module.

    Right click the dll file and find version in the file properties.

    in reply to: Multilanguage on Schemes #7395
    Mikhail
    Moderator

    Currently, you should create separate scheme for each language, and setup roles to show only necessary schemes for a user. To change phrases in the same scheme (or table) some kind of built-in dictionary should be implemented. It’s an interesting idea, but it might be expensive to develop.

    in reply to: BACnet KP #7394
    Mikhail
    Moderator

    The ScadaCommCommon must change, because I have changed some code in the UDPTransport so it can work with BACnet, ScadaData can remove

    If every driver had its own ScadaCommCommon.dll, it would be impossible to use the software. We should merge the changes if they are compatible, or the UDP implementation should be made inside the driver. Could you show what was changed in ScadaCommCommon?

    Note: In the version 6, you can add new communication channels to resolve such cases easier.

    in reply to: Blending out navigation mene items #7385
    Mikhail
    Moderator

    Hi,

    You right. Roles don’t affect this menu. To hide the Plugins menu item (for all), you could deactivate Store and Configurator plugins.

    in reply to: Multilanguage on Schemes #7384
    Mikhail
    Moderator

    Hi,

    To translate scheme and tables, you should add language files in the directories
    C:\SCADA\ScadaWeb\plugins\Scheme\lang\
    C:\SCADA\ScadaWeb\plugins\Table\lang\

    Did I understand you correctly? Or may be you are talking about translating a scheme text labels that are placed by an engineer?

    in reply to: BACnet KP #7383
    Mikhail
    Moderator

    Hi,

    I have made a BACnet KP for Rapid Scada to work with BACnet devices.

    Great!

    May I ask a few questions:
    1. Why do you include ScadaCommCommon.dll and ScadaData.dll into the archive? Is it possible to remove them because they are already exist in the destination directories?

    2. What is the pricing? Which license types are available?

    3. May be it would be useful if you add version number in the archive name, e.g. KpBACnet_5.0.0.0.zip

    We would be glad to publish your driver in the repository after clarifying the above questions.

    in reply to: Access Rapid SCADA data from Node-RED #7382
    Mikhail
    Moderator

    trend.LastFillTime = DateTime.UtcNow;

    Does it affect something?

    in reply to: Server problem #7380
    Mikhail
    Moderator

    Also please check version of Automatic Control Module.
    Please make a screenshot of the trigger that sends commands every minute.

    • This reply was modified 5 years, 3 months ago by Mikhail.
    in reply to: Server problem #7379
    Mikhail
    Moderator

    Looks like is hangs.

    1. Why do you have so many commands? What do they do?
    2. What was the first timestamp when Communicator couldn’t connect?

    in reply to: Multilanguage on Schemes #7369
    Mikhail
    Moderator

    Hi,

    Sure. Everything can be translated. If you’re asking for advice how to do it, I can help.

    in reply to: Access Rapid SCADA data from Node-RED #7368
    Mikhail
    Moderator

    @kumajaya thank you for your help. It is very useful. We will check this.

    in reply to: Server problem #7367
    Mikhail
    Moderator

    What is the SCADA-Server version?

    in reply to: Server problem #7366
    Mikhail
    Moderator

    Hello,

    Application shutdown means that the web server stops the web application. It is not related to SCADA-Server.

    When the server is in error state, what is written in server and communicator logs?