Issue with Comm Line Termination

Forum Home Forums Uncategorized Issues Issue with Comm Line Termination

Viewing 7 posts - 1 through 7 (of 7 total)
  • Author
    Posts
  • #14729
    tristansth
    Participant

    Our modbus communication line shows as ‘Terminated’ under its Line State, and in the Line Log it shows as having stopped itself.

    I have been unable to get it to start back up and would appreciate any assistance with this issue.

    #14730
    zzz
    Participant

    What is “having stopped itself” ? Are you talking about modbus TCP/RTU, which variant? Is this an working instance with new issue or an fresh new setup ?

    PS: There is option named Poll only on command in LineOptions>DevicePolling make sure it not ticked.

    • This reply was modified 4 months, 3 weeks ago by zzz.
    #14734
    tristansth
    Participant

    The ‘Line Log’ for the Modbus TCP Communication Line has the following as its latest entry: “2024-04-11 15:02:50 Communication line [2] Modbus_TCP is stopped”

    This was a previously working instance set up by the previous tech that I’m now trying to get back up and running.

    DevicePolling is not ticked for any of the devices, but its not a device issue, it’s the entire Line.

    #14740
    Mikhail
    Moderator

    Hello,
    When the Communicator service starts, it starts all lines. If some line is not started, the info is written in ScadaComm.log
    Try restarting the Communicator service and check ScadaComm.log for errors.

    #14741
    Mikhail
    Moderator

    Make sure that the line is still active.

    #14757
    tristansth
    Participant

    Thank you for the assistance, managed to resolve this issue.

    One of the devices in the line was set up to use a module that wasn’t installed for some reason. Removed the device and the line is polling fine again.

    #14766
    Mikhail
    Moderator

    🙂