Gensets controllers monitor using Rapidscada

Forum Home Forums Communicating with Devices Gensets controllers monitor using Rapidscada

Tagged: 

Viewing 6 posts - 1 through 6 (of 6 total)
  • Author
    Posts
  • #5967
    Osama73
    Participant

    Dears,

    I looking for your support the steps must do to cummincate between Gensets controllers DSE 7320 and rapid scada.
    First question is it possible
    Second if yes what must i do..??

    Thank you in advance for your clarification.
    Best regards
    Osama

    #5970
    Mikhail
    Moderator

    Hello,

    DSE 7320 supports Modbus communication protocol, so it can be connected to Rapid SCADA.

    You should do the following:
    1. Read this article and watch this video.
    2. Create your own simple project to read data from Modbus simulator.
    3. Find the Modbus register map for DSE 7320 in the manufacturers documentation.
    4. Create your Modbus template DSE 7320 for that specifies the registers to read.

    #5971
    Mikhail
    Moderator

    I’ve got a Modbus template for some model of DSE controller. I can share it in case you will share the final template for DSE 7320.

    #5974
    Osama73
    Participant

    Hi mickel,

    Thank you for your valuable resources

    If tge genset get controller support TCP / IP
    Can i extract data from them? Or must use modbus port?.

    Am i need external gateway or only connect Modbus port from DSE 7320 into Rapid scada software using Modbus serial converter??

    Please advice
    Best regards
    Osama

    #5975
    Mikhail
    Moderator

    Hi,

    Can i extract data from them? Or must use modbus port?.

    Please read the manual. Likely, you can use Modbus TCP.

    First, try to use built-in Ethernet port of the controller if it is presented. I’m not DSE guru, but talk from common point of view.

    #5977
    Osama73
    Participant

    Thank you michel for your fast response