Forum Home › Forums › Communicating with Devices › OPC › Disconnect from OPC DA server
Tagged: dcom OPC-DA
- This topic has 6 replies, 3 voices, and was last updated 3 weeks, 2 days ago by
RhysGoodwin.
-
AuthorPosts
-
May 2, 2025 at 1:35 pm #16386
xujiujing
ParticipantHi everyone,
I am trying to set up a DA to UA Gateway.
Rapidscada and the OPC DA Server are running on different machines.
Communicator and Agent applications were installed on the remote PC.
The ScadaComm6 service was setup to work as the OPCSrv user. Such as this.
The driver is DrvOpcClassic 6.0.1.2.
Rapidscada version is 6.4.1.
It seems Rapidscada could read the variables from the OPC DA server.
However, I got the following error messages after I closing the device property settings (Device Polling):
——————————————————————————–
(Log messages in communication lines)
——————————————————————————–
2025-05-02 21:29:49 Start communication line [1] opcda2025-05-02 21:29:49 Connect to Matrikon.OPC.Simulation/{f858xxxx-xxxx-xxxx-xxxx-00c0f010xxxx}
Connection to the OPC DA server has been established2025-05-02 21:29:50 Create subscriptions
Create subscription “” for the device [1] Matrikon (async)
Error creating subscriptions:
0x800402022025-05-02 21:31:07 Disconnect from OPC DA server
2025-05-02 21:31:07 Error disconnecting OPC DA server:
0x800402002025-05-02 21:31:07 Communication line [1] opcda is stopped
——————————————————————————–Would you please help me solve this problem?
Thanks a lot in advance!May 5, 2025 at 11:29 am #16388
MikhailModeratorHi,
> Rapidscada and the OPC DA Server are running on different machines.
When OPC DA server and client are installed on different machines, it requires setup of DCOM security. You should search for DCOM manuals. Sometimes a user manages to run it.
I recommend installing Communicator on the same machine where the OPC server is already installed.May 6, 2025 at 3:55 am #16390xujiujing
ParticipantHi Mikhail,
Thanks a lot for your reply. My DCOM configuration was reset by accident. I’ve now managed to get everything working again.
Many thanks for your support and guidance.
Best regards
Jiujing XuJune 12, 2025 at 8:39 am #16483xujiujing
ParticipantHi Mikhail,
I am performing the same task with another OPC DA server running on a different machine.
DCOM configuration has already been completed.
Using the “MatrikonOPC Explorer” OPC DA client, I am able to successfully connect to the remote OPC DA server. However, when attempting to access the server using Rapid SCADA, I encounter an error: “CoCreateInstanceEx denies access.”
Both machines have installed the following components:
OPC Core Components Redistributable (x64) 3.00.108
OPC Core Components Redistributable (x86) 3.00.108Could you please advise on how to resolve this issue?
Thank you very much for your help in advance. Wishing you a great day!Best regards,
Jiujing XuJune 13, 2025 at 2:04 am #16484xujiujing
ParticipantHi Mikhail,
Sorry to bother you again. It seems that my OpcEnum configuration has been changed once more. The connection is working fine now.
Best regards,
Jiujing XuJune 13, 2025 at 5:47 am #16485
MikhailModeratorHi,
Thanks a lot for the update.November 17, 2025 at 10:57 pm #17317RhysGoodwin
ParticipantHi,
For others who come across this, some hopefully usful tips for using Rapid SCADA to connect to a remote OPC-DA server in a workgroup (non-domain joined) environment.
– Create local accounts with matching username and passwords on both servers
– On the OPC-DA server side:
– Ensure the user has sufficient decom permissions
– Ensure SID filtering is disabled:
HKEY_LOCAL_MACHINE\SOFTWARE\Microsoft\Windows\CurrentVersion\Policies\System
LocalAccountTokenFilterPolicy=1– On the Rapid SCADA server:
– Make the local user an admin (at least for testing, it may be possible to lock it down later)
– Make sure to run the Rapid SCADA admin tool as this local user
– Make sure to run the Rapid SCADA ScadaComm6 system service as this user
– Set app-specific DCOM authentication for ScadaComm6 with the following reg import:This should fix `Error creating subscriptions:
0x80040202`Windows Registry Editor Version 5.00 ; Make your own GUI with PowerShell: [guid]::NewGuid() ; Tie the EXE to an AppID (so it appears under DCOM Config) [HKEY_CLASSES_ROOT\AppID\ScadaCommWkr.exe] "AppID"="{9a9a27c6-3317-405a-a364-ce4eb1878a95}" ; Define the AppID node with a friendly name (what you’ll see in DCOMCNFG) [HKEY_CLASSES_ROOT\AppID\{9a9a27c6-3317-405a-a364-ce4eb1878a95}] @="Rapid SCADA - ScadaComm Worker (OPC-DA Client)" ; Optional: per-app authentication level. 0=Default, 1=None, 2=Connect, 3=Call, 4=Pkt, 5=PktIntegrity, 6=PktPrivacy. "AuthenticationLevel"=dword:00000001Cheers,
Rhys -