April 1, 2021 at 9:39 am #8618afzalParticipant
Hi,
i am communicating through modbus, my slave devices are sending data at the interval of some milliseconds but scada is receiving after 2 seconds or sometimes after 4 seconds.
i have already set current data setting “On Change”
why scada is slow to receive the data ?
if it can communicate to 65535 device, it should not feel any burden.
where could be the problem ?Regards
AfzalApril 1, 2021 at 12:46 pm #8622MikhailModeratorHi,
Please provide communication line log.
April 1, 2021 at 1:53 pm #8628afzalParticipanti place the communication log below.
2021-04-01 15:47:15 Communication session with the Device 1 “IN_TEMP”, type: KpModbus, address: 1
Request element group “TEMPERATURE”
Send (8): 01 03 11 93 00 0A 30 DC
Receive (5/5): 01 03 14 08 34
Receive (20/20): 08 2A 00 0A 00 0A 00 14 00 2D 00 28 00 32 00 3C 00 46 83 84
OK!2021-04-01 15:47:16 Communication session with the Device 2 “IN_FLOW”, type: KpModbus, address: 2
Request element group “Flow”
Send (8): 02 04 0D AB 00 05 43 76
Receive (5/5): 02 04 0A 04 0B
Receive (10/10): 03 77 03 61 03 6B 03 75 AC 3D
OK!2021-04-01 15:47:16 Communication session with the Device 3 “IN_PRESSURE”, type: KpModbus, address: 3
Request element group “PRESSURE”
Send (8): 03 03 09 C3 00 05 77 8B
Receive (5/5): 03 03 0A 03 4D
Receive (10/10): 03 57 03 61 03 6B 03 75 D1 0C
OK!2021-04-01 15:47:17 Communication session with the Device 4 “OUT_SENECA_DO”, type: KpModbus, address: 4
No elements for request2021-04-01 15:47:17 Communication session with the Device 5 “OUT_POMPA_A”, type: KpModbus, address: 5
No elements for request2021-04-01 15:47:17 Communication session with the Device 6 “OUT_POMPA_B”, type: KpModbus, address: 6
No elements for request2021-04-01 15:47:18 Communication session with the Device 1 “IN_TEMP”, type: KpModbus, address: 1
Request element group “TEMPERATURE”
Send (8): 01 03 11 93 00 0A 30 DC
Receive (5/5): 01 03 14 08 38
Receive (20/20): 08 2E 00 0A 00 0A 00 14 00 2D 00 28 00 32 00 3C 00 46 D2 14
OK!2021-04-01 15:47:18 Communication session with the Device 2 “IN_FLOW”, type: KpModbus, address: 2
Request element group “Flow”
Send (8): 02 04 0D AB 00 05 43 76
Receive (5/5): 02 04 0A 04 0F
Receive (10/10): 03 7B 03 65 03 6F 03 79 E2 F9
OK!2021-04-01 15:47:19 Communication session with the Device 3 “IN_PRESSURE”, type: KpModbus, address: 3
Request element group “PRESSURE”
Send (8): 03 03 09 C3 00 05 77 8B
Receive (5/5): 03 03 0A 03 52
Receive (10/10): 03 5C 03 66 03 70 03 7A 62 3F
OK!2021-04-01 15:47:19 Communication session with the Device 4 “OUT_SENECA_DO”, type: KpModbus, address: 4
No elements for request2021-04-01 15:47:19 Communication session with the Device 5 “OUT_POMPA_A”, type: KpModbus, address: 5
No elements for request2021-04-01 15:47:20 Communication session with the Device 6 “OUT_POMPA_B”, type: KpModbus, address: 6
No elements for requestif you observe, Device 1 data come for 15:47:15 then 15:47:18, 2 seconds are missing.
April 2, 2021 at 1:47 pm #8631MikhailModeratorFor instance, Device 1 “IN_TEMP” is polled every 3 seconds. To increase data refresh rate, you need to increase polling speed. Check delays in Communicator settings.
-