Communicator error “unable to read data packet header”

Forum Home Forums Runtime Bugs Communicator Bugs Communicator error “unable to read data packet header”

Viewing 8 posts - 1 through 8 (of 8 total)
  • Author
    Posts
  • #15310
    OPCUser
    Participant

    Hi Mikhail,

    i ran into a problem today. Communicator stopped working
    all of a sudden giving me the error: “Error checking server connection:
    Incorrect format of data received from the server: unable to read data packet header”

    Here is the communicator log:

    ——————————————————————————–
    2024-09-05 15:47:44 [OPC-WINCC][OPCSrv][ACT] Communicator 6.2.0.0 started
    2024-09-05 15:47:44 [OPC-WINCC][OPCSrv][ACT] Storage FileStorage 6.2.0.0 loaded from file C:\Program Files\SCADA\ScadaComm\FileStorage.dll
    2024-09-05 15:47:44 [OPC-WINCC][OPCSrv][ACT] Start logic processing
    2024-09-05 15:47:44 [OPC-WINCC][OPCSrv][ACT] Driver DrvDsOpcUaServer 6.0.0.2 loaded from file C:\Program Files\SCADA\ScadaComm\Drv\DrvDsOpcUaServer.Logic.dll
    2024-09-05 15:47:44 [OPC-WINCC][OPCSrv][ACT] Driver DrvDsScadaServer 6.0.1.1 loaded from file C:\Program Files\SCADA\ScadaComm\Drv\DrvDsScadaServer.Logic.dll
    2024-09-05 15:47:44 [OPC-WINCC][OPCSrv][ACT] Driver DrvOpcClassic 6.0.1.2 loaded from file C:\Program Files\SCADA\ScadaComm\Drv\DrvOpcClassic.Logic.dll
    2024-09-05 15:47:44 [OPC-WINCC][OPCSrv][ACT] Data source ScadaServer initialized successfully
    2024-09-05 15:47:44 [OPC-WINCC][OPCSrv][ACT] Data source OpcUaServer initialized successfully
    2024-09-05 15:47:45 [OPC-WINCC][OPCSrv][ACT] Data source ScadaServer: Receive the configuration database
    2024-09-05 15:47:47 [OPC-WINCC][OPCSrv][ERR] Data source ScadaServer: Error checking server connection:
    Incorrect format of data received from the server: unable to read data packet header
    2024-09-05 15:47:47 [OPC-WINCC][OPCSrv][ERR] Unable to start communication lines because the configuration database is not received
    2024-09-05 15:47:49 [OPC-WINCC][OPCSrv][ACT] Stop communication lines
    2024-09-05 15:47:49 [OPC-WINCC][OPCSrv][ACT] All communication lines are stopped
    2024-09-05 15:47:49 [OPC-WINCC][OPCSrv][ACT] Logic processing is stopped
    2024-09-05 15:47:49 [OPC-WINCC][OPCSrv][ACT] Communicator is stopped
    ——————————————————————————–

    Can you point me to where the problem is?

    Thanks in advance.

    David

    #15319
    Mikhail
    Moderator

    Hi,

    A possible reason is that TCP port 10000 has started to be used by another application, not the Server app.

    #15340
    OPCUser
    Participant

    Hi there,

    you were right, i had added influxDB as a datasource to grafana on the machine thats running RapidSCADA and Grafana.
    I changed the port of Server and Communicator to 10003 (10001 and 10002 wasnt working for me) and then it was fine again.

    Thank you,

    David

    #15366
    Mikhail
    Moderator

    Hi,

    That’s good.
    I suggest TCP View utility to check all ports in use.

    #18093
    elee
    Participant

    Hello,

    I am having the same error, here are the logs:

    During the Uploads:
    Transfer configuration
    Archive size: 157,059 bytes

    Stop the Communicator service
    Service control command failed
    Stop the Webstation service
    Service control command completed successfully
    Restart the Server service
    Service control command completed successfully
    Start the Communicator service
    Service control command failed
    Start the Webstation service
    Service control command completed successfully

    Configuration uploaded successfully

    ScadaComm.log:
    ——————————————————————————–
    2026-06-25 14:58:42 [webserver][root][ACT] Communicator 6.2.0.1 started
    2026-06-25 14:58:42 [webserver][root][ACT] Storage FileStorage 6.4.0.0 loaded from file /opt/scada/ScadaComm/FileStorage.dll
    2026-06-25 14:58:42 [webserver][root][ACT] Start logic processing
    2026-06-25 14:58:42 [webserver][root][ACT] Driver DrvCnlBasic 6.1.0.1 loaded from file /opt/scada/ScadaComm/Drv/DrvCnlBasic.Logic.dll
    2026-06-25 14:58:42 [webserver][root][ACT] Driver DrvDsScadaServer 6.0.1.1 loaded from file /opt/scada/ScadaComm/Drv/DrvDsScadaServer.Logic.dll
    2026-06-25 14:58:42 [webserver][root][ACT] Driver DrvModbus 6.0.0.5 loaded from file /opt/scada/ScadaComm/Drv/DrvModbus.Logic.dll
    2026-06-25 14:58:42 [webserver][root][ACT] Driver DrvSnmp 6.0.0.1 loaded from file /opt/scada/ScadaComm/Drv/DrvSnmp.Logic.dll
    2026-06-25 14:58:42 [webserver][root][ACT] Data source ScadaServer initialized successfully
    2026-06-25 14:58:42 [webserver][root][ACT] Data source ScadaServer: Receive the configuration database
    2026-06-25 14:58:42 [webserver][root][ACT] Data source ScadaServer: The configuration database has been received successfully
    2026-06-25 14:58:42 [webserver][root][ACT] Start communication lines
    2026-06-25 14:58:42 [webserver][root][ACT] Start reading commands from files
    2026-06-25 14:58:42 [webserver][root][ACT] Data source ScadaServer: Connection state is Logged In
    2026-06-25 15:00:00 [webserver][root][ACT] Stop communication lines
    2026-06-25 15:00:09 [webserver][root][ERR] Data source ScadaServer: Error receiving telecontrol commands:
    Incorrect format of data received from the server: unable to read data packet header
    2026-06-25 15:00:09 [webserver][root][ACT] Data source ScadaServer: Connection state is Error
    2026-06-25 15:00:09 [webserver][root][ERR] Data source ScadaServer: Error receiving telecontrol commands:
    Unable to write data to the transport connection: Broken pipe.
    2026-06-25 15:00:09 [webserver][root][ERR] Data source ScadaServer: Error receiving telecontrol commands:
    Connection refused [::ffff:10.1.10.141]:10000
    2026-06-25 15:00:09 [webserver][root][ACT] Unable to stop logic processing for a specified time
    2026-06-25 15:00:09 [webserver][root][ACT] Communicator is stopped
    ——————————————————————————–
    2026-06-25 15:00:10 [webserver][root][WARN] Following communication lines are still working: 2
    ——————————————————————————–
    2026-06-25 15:00:52 [webserver][root][ACT] Communicator 6.2.0.1 started
    2026-06-25 15:00:52 [webserver][root][ACT] Storage FileStorage 6.4.0.0 loaded from file /opt/scada/ScadaComm/FileStorage.dll
    2026-06-25 15:00:52 [webserver][root][ACT] Start logic processing
    2026-06-25 15:00:52 [webserver][root][ACT] Driver DrvCnlBasic 6.1.0.1 loaded from file /opt/scada/ScadaComm/Drv/DrvCnlBasic.Logic.dll
    2026-06-25 15:00:52 [webserver][root][ACT] Driver DrvDsScadaServer 6.0.1.1 loaded from file /opt/scada/ScadaComm/Drv/DrvDsScadaServer.Logic.dll
    2026-06-25 15:00:52 [webserver][root][ACT] Driver DrvModbus 6.0.0.5 loaded from file /opt/scada/ScadaComm/Drv/DrvModbus.Logic.dll
    2026-06-25 15:00:52 [webserver][root][ACT] Driver DrvSnmp 6.0.0.1 loaded from file /opt/scada/ScadaComm/Drv/DrvSnmp.Logic.dll
    2026-06-25 15:00:52 [webserver][root][ACT] Data source ScadaServer initialized successfully
    2026-06-25 15:00:52 [webserver][root][ACT] Data source ScadaServer: Receive the configuration database
    2026-06-25 15:00:52 [webserver][root][ACT] Data source ScadaServer: The configuration database has been received successfully
    2026-06-25 15:00:52 [webserver][root][ACT] Start communication lines
    2026-06-25 15:00:53 [webserver][root][ACT] Start reading commands from files
    2026-06-25 15:00:53 [webserver][root][ACT] Data source ScadaServer: Connection state is Logged In

    When searching for active ports on the server sudo ss -tulpn
    it only shows dotnet as using 10000/8/2
    When searching for 10000, sudo ss -tulpn | grep 10000
    it shows dotnet but the port is in red…

    Thank you for your help!

    #18096
    elee
    Participant

    Edit: this issue is intermittent when uploading configurations

    #18098
    Mikhail
    Moderator

    > Stop the Communicator service
    > Service control command failed
    The above messages indicate that Communicator is taking too long to stop.

    > 2026-06-25 15:00:10 [webserver][root][WARN] Following communication lines are still working: 2
    This one similar.

    What does line #2 do?
    It should be optimized.

    #18101
    elee
    Participant

    Line 2 has TCP connection timeout errors, how can I optimize this line? There are 4 snmp devices. I can move one to modbus (line 1), as that device has both options, the others do not. What is the maximum number of devices per line?

    Is it fair to assume that each communication line should have all devices of that driver type assigned?

    Line 2 Main Options: (program defaults)
    request retries on error – 3
    delay after polling cycle – 0
    TCP Client, reconnectAfter = 5

    Line 2 Custom Options:
    TansMode = TCP

    Line 2 Device Polling: (program defaults)
    Timeout = 1000
    Delay = 200
    Time = 0
    Period = 0
    Command Line = (blank)