Communication error: receiving data from device

Forum Home Forums Communicating with Devices Communication error: receiving data from device

Viewing 11 posts - 1 through 11 (of 11 total)
  • Author
    Posts
  • #10295
    Thov
    Participant

    Hi, it seems I’m having trouble with receiving data over MOD-bus as I get continually “Communication error!” in the line stats. I’ve used Simply Modbus Master to verify that the devices do communicate properly, so it seems the issue is within my Rapid Scada settings.

    Line 1 stats:
    https://imgur.com/gallery/PSCxjkA

    Simply Modbus Master:
    https://imgur.com/gallery/3OLPps2

    Serial port settings:ยจ
    https://imgur.com/gallery/kLQBXMz

    Sincerely
    Thov

    #10296
    Thov
    Participant

    I can also add that the device debugger prints request info when Rapid Scada requests data from it, as seen in the lines “RegCoilCB rd: 1, N …” :
    https://imgur.com/gallery/YM63sYi

    #10297
    Mikhail
    Moderator

    Hi,

    Please send a screenshot of the device properties in Communicator.
    Do you use Modbus RTU via COM-port or Modbus TCP?

    #10298
    Thov
    Participant

    Hi,

    I hope these are the device properties you requested:
    https://imgur.com/gallery/pxFga5t

    I use Modbus RTU via COM-port.

    #10299
    Mikhail
    Moderator

    Thanks.
    Set Call Number to empty in the device settings in Communicator and in the Device table of the configuration database.
    Also set Period to zero.
    Then upload the project to run.

    If doesn’t work, send new logs.

    #10300
    Mikhail
    Moderator

    Keep only 1 device active to make tests clear.

    #10301
    Thov
    Participant

    Done, but no change. The device still outputs that it receives the requests from Rapid Scada as before.
    Line 1 parameters:
    https://imgur.com/gallery/lpEA0kS

    Devices:
    https://imgur.com/gallery/dBnIxdR

    Line 1 stats:
    https://imgur.com/gallery/ilVwN3u

    #10302
    Mikhail
    Moderator

    Now it is better.
    Copy the request as a text here (Ctrl+C).
    Then compare requests in Communicator and in Simply Modbus Master by this tool.

    #10303
    Mikhail
    Moderator

    You should set Address in the Devices table.

    #10304
    Thov
    Participant

    Alright, it seems things have been solved:

    I used your linked site and input the request first from Rapid Scada (00 01 00 01 00 10 6D D7) and got this:
    00 Slave address 0x00 (0)
    01 Function code 0x01 (1) – Read Coils
    00 01 Starting address Physical: 0x0001 (1)
    Logical: 0x0002 (2)
    00 10 Quantity 0x0010 (16)
    6D D7 CRC 0x6DD7 (28119)

    Then I did the same for a working coil request from Simply Modbus Master (01 01 00 00 00 10 3D C6) and got this:
    01 Slave address 0x01 (1)
    01 Function code 0x01 (1) – Read Coils
    00 00 Starting address Physical: 0x0000 (0)
    Logical: 0x0001 (1)
    00 10 Quantity 0x0010 (16)
    3D C6 CRC 0x3DC6 (15814)

    So the slave address was mismatching. I then went to Configurator Database -> Devices and set the address of the masterboard to 1:
    https://imgur.com/gallery/p35RlR9

    I then reuploaded, and got successful data from masterboard (device nr. 1)!
    https://imgur.com/gallery/IYeezme

    Then I did the same as the previous step for the other two devices (device nr. 2 and 3), i.e. Configurator Database -> Devices and set their addresses to 1 as well. BUT: I left their Call numbers as 127.0.0.1. Remember that I set the Call number for device nr. 1 to blank as per your request at 2:06pm.

    Then I set them to be active again in Instances -> Default -> Communicator -> Communication lines -> Line 1 parameters:
    https://imgur.com/gallery/Rw9A1qP

    Then I reuploaded, and now I have all data coming from my devices, so we’re back in business ๐Ÿ™‚

    For the record, I don’t yet know precisely what I did wrong the first time or why it did not work, but I see that the addresses need to match, obviously – you probably have a better idea about why.

    #10305
    Mikhail
    Moderator

    The preferable address is taken from the configuration database.
    However, it’s more clear when the addresses matched. It’s possible to sync addresses by a tool after they changed manually.