Communication

Forum Home Forums Communicating with Devices Modbus Communication

Viewing 9 posts - 1 through 9 (of 9 total)
  • Author
    Posts
  • #571
    brijesh
    Participant

    We are able to communicate with Conzerv Energy Meter EM6400, but in the SCADA communicator the value (Float) shows continuously increasing, wraps after showing a very large number and again starts from 0.000 ? What is this ? Please help.

    When we use MODSCAN software, the same meter gives stable value on the scren. But with Rapid scada above problem appears. The catalog of the meter says, it is direct and no conversion required.

    #572
    Mikhail
    Moderator

    Hi,
    Can you post here a part of communication line log? And the expected value.
    If it is possible also provide MODSCAN log for comparison.

    #573
    brijesh
    Participant

    In case of MODSCAN it gives as the real value (Register 3925 3926, total 32 bit) as 212.560 volts, while in case of Rapid SCADA communicator the value varies randomly and wraps after a very large value.say it is like 323,435,234,011,234,123.000.

    #574
    brijesh
    Participant

    When I take the data value from Line Log (Data Receive Values) in the communicator, and put those values in Hex to Float Converter (Outside SCADA Calculator), then it gives me the correct value. That means whatever value I am getting is in Hex Only, and I need to apply the Hex to Float conversion. Kindly let me know, how I can do that.

    #575
    Mikhail
    Moderator

    I would like to see the log.

    #576
    brijesh
    Participant

    2015-10-03 16:44:42 Communication session with the Device 41 “EM6400-1”, type: KpModbus, address: 1
    Request element group “Energy Management 1”
    Send (8): 01 03 0F 62 00 02 66 C1
    Receive (5/5): 01 03 04 FE 05
    Receive (4/4): 43 D0 EB 76
    OK!

    Now this 43 D0 EB 76 is ok value but in Hex….We want to convert that in Float (Real Value), MODSCAN shows the correct value on the terminal that is 417.839.

    We have selected Float(4 Byte) in communication template…

    #577
    Mikhail
    Moderator

    EB 76 is the checksum
    43 D0 FE 05 is the value 417.984528
    You should set the correct bytes order in Device Template Editor.
    Try the order 2301.
    Please notify me about the result.

    #578
    brijesh
    Participant

    Thank you Mikhail, now its ok…

    I have around 60 such values, I have understood the commncation configuration part etc, now I wish to bring all of them to an .xls (excel file), please guide how that can be done. Regards….

    #579
    Mikhail
    Moderator

    OK, create a separate topic please.

Viewing 9 posts - 1 through 9 (of 9 total)