  • in reply to: MQTT in-depth Installation Help #6275
    phachakorn
    Participant

    to greenfoxx
    it Works.
    Thanks you.

    in reply to: MQTT in-depth Installation Help #6262
    phachakorn
    Participant

    I also encountered the same problem.

    This message in Line Log

    2019-12-25 13:40:25 Error executing actions of Device 52 “MQTT” on communication line terminating: Object reference not set to an instance of an object.

    2019-12-25 13:40:25 Stop communication line 6 “MQTT”
    ——————————————————————————–
    ——————————————————————————–
    2019-12-25 13:43:47 Initialize communication line 6 “MQTT”
    2019-12-25 13:43:47 Error executing actions of Device 52 “MQTT” on adding device to communication line: Could not find a part of the path ‘C:\SCADA\ScadaComm\Config\’.
    2019-12-25 13:43:47 Start communication line 6 “MQTT”

    2019-12-25 13:43:47 Communication session with the Device 52 “MQTT”, type: KpMqtt
    Error reconnecting

    2019-12-25 13:43:47 Communication session with the Device 52 “MQTT”, type: KpMqtt
    Error reconnecting

    2019-12-25 13:43:47 Communication session with the Device 52 “MQTT”, type: KpMqtt
    Error reconnecting

    2019-12-25 13:43:47 Communication session with the Device 52 “MQTT”, type: KpMqtt
    Error reconnecting

    in reply to: I can not Activate Installed Plugins. #4306
    phachakorn
    Participant

    It works.
    Solved the problem.
    Thanks for the quick advice.

    in reply to: I can not Activate Installed Plugins. #4292
    phachakorn
    Participant

    I use OS windows server 2012R2

    in reply to: Please advise Extra Scheme Components Plugin #4274
    phachakorn
    Participant

    It works.
    Solved the problem.
    Thanks for the quick advice.

    in reply to: Please advise Extra Scheme Components Plugin #4268
    phachakorn
    Participant

    Hi Mikhail.
    Thank you for your advice.
    My name is Phachakorn
    I use Scheme Editor Version 5.2.2.0

    This is a message from Log file.
    ——————————————————————————–
    2561-09-17 18:17:17 <PNT-PC><PNT><ACT> Initialize common data of Scheme Editor
    2561-09-17 18:17:17 <PNT-PC><PNT><ACT> Load components from files
    2561-09-17 18:17:17 <PNT-PC><PNT><ACT> Components are loaded from the file C:\SCADA\ScadaWeb\bin\PlgSchBasicComp.dll
    2561-09-17 18:17:17 <PNT-PC><PNT><ERR> Error loading the plugin assembly C:\SCADA\ScadaWeb\bin\PlgSchExtraComp.dll:
    Could not load file or assembly ‘file:///C:\SCADA\ScadaWeb\bin\PlgSchExtraComp.dll’ or one of its dependencies. Operation is not supported. (Exception from HRESULT: 0x80131515)
    2561-09-17 18:17:17 <PNT-PC><PNT><ACT> WCF service is started
    2561-09-17 18:28:30 <PNT-PC><PNT><ACT> WCF service is stopped
    2561-09-17 18:28:30 <PNT-PC><PNT><ACT> Scheme Editor is shutdown
    ——————————————————————————–

    What do I have to do Advise me.

    Thanks You.
    Phachakorn Tasusee
    Head of Automation Department
    Quick ERP Co., Ltd.

    in reply to: Numbers can not be seen in the table. #2100
    phachakorn
    Participant

    p1

    in reply to: Numbers can not be seen in the table. #2098
    phachakorn
    Participant

    hi
    i checked all number of year is 2017 all data but number in WEB table view not show.

    Do I have to fix anything else?

    in reply to: Numbers can not be seen in the table. #2066
    phachakorn
    Participant

    hi
    I do as you suggest. It gives the Hourly file a valid year name (170331.dat) . And in the log file, the year number is 2017.
    But in the table on the web SCADA that do not have the numbers.

    Do I have to fix anything else?

    in reply to: Numbers can not be seen in the table. #2055
    phachakorn
    Participant

    Hi
    In Thailand, there are two year count systems.
    Buddhist era and Christian era.
    2560 is Buddhist era count systems.
    But in computer i setup Legion and Language format to Christian era.
    Do I need to set up another one?

    I see C:\SCADA\ScadaComm\Log\ScadaCommSvc.log have 2560 year too.

    I will try to follow this advice.
    “Try opening Control Panel > Administrative Tools > Services and changing the user for ScadaServerService and ScadaCommService”

    thanks you

    in reply to: Numbers can not be seen in the table. #2053
    phachakorn
    Participant

    HI
    mine

    ——————————————————————————–
    2560-03-27 15:46:18 <SCADA-PC><SYSTEM><ACT> ScadaServerService 5.0.1.0 is started
    2560-03-27 15:46:19 <SCADA-PC><SYSTEM><ACT> Check the existence of the data directories is completed successfully
    2560-03-27 15:46:19 <SCADA-PC><SYSTEM><ACT> Check the existence of the configuration database files is completed successfully
    2560-03-27 15:46:19 <SCADA-PC><SYSTEM><ACT> Input channels are read from the configuration database. Active channel count: 40
    2560-03-27 15:46:19 <SCADA-PC><SYSTEM><ACT> Ouput channels are read from the configuration database
    2560-03-27 15:46:19 <SCADA-PC><SYSTEM><ACT> Users are read from the configuration database
    2560-03-27 15:46:20 <SCADA-PC><SYSTEM><ACT> Formulas are read from the configuration database
    2560-03-27 15:46:29 <SCADA-PC><SYSTEM><ACT> The formulas source code has been compiled
    2560-03-27 15:46:29 <SCADA-PC><SYSTEM><ACT> Connection listener is started
    2560-03-27 15:46:29 <SCADA-PC><SYSTEM><ACT> Start server
    2560-03-27 15:46:29 <SCADA-PC><SYSTEM><ACT> Current data are not loaded
    2560-03-27 15:46:32 <SCADA-PC><SYSTEM><ACT> Connect to client 127.0.0.1
    2560-03-27 15:46:32 <SCADA-PC><SYSTEM><ACT> The user ScadaComm is successfully authenticated
    2560-03-27 22:28:32 <SCADA-PC><SYSTEM><ACT> Connect to client 127.0.0.1
    2560-03-27 22:28:32 <SCADA-PC><SYSTEM><ACT> The user ScadaWeb is successfully authenticated
    2560-03-27 22:29:27 <SCADA-PC><SYSTEM><ACT> Check user admin name and password. Result: passed
    2560-03-27 22:30:57 <SCADA-PC><SYSTEM><ACT> Disconnect client 127.0.0.1
    2560-03-27 22:38:02 <SCADA-PC><SYSTEM><ACT> Connect to client 127.0.0.1
    2560-03-27 22:38:02 <SCADA-PC><SYSTEM><ACT> The user ScadaComm is successfully authenticated
    2560-03-27 22:38:39 <SCADA-PC><SYSTEM><ACT> Connection listener is stopped
    2560-03-27 22:38:39 <SCADA-PC><SYSTEM><ACT> Server is stopped
    2560-03-27 22:38:39 <SCADA-PC><SYSTEM><ACT> ScadaServerService is stopped
    ——————————————————————————–
    ——————————————————————————–
    2560-03-27 22:38:40 <SCADA-PC><SYSTEM><ACT> ScadaServerService 5.0.1.0 is started
    2560-03-27 22:38:40 <SCADA-PC><SYSTEM><ACT> Check the existence of the data directories is completed successfully
    2560-03-27 22:38:41 <SCADA-PC><SYSTEM><ACT> Check the existence of the configuration database files is completed successfully
    2560-03-27 22:38:41 <SCADA-PC><SYSTEM><ACT> Input channels are read from the configuration database. Active channel count: 40
    2560-03-27 22:38:41 <SCADA-PC><SYSTEM><ACT> Ouput channels are read from the configuration database
    2560-03-27 22:38:41 <SCADA-PC><SYSTEM><ACT> Users are read from the configuration database
    2560-03-27 22:38:41 <SCADA-PC><SYSTEM><ACT> Formulas are read from the configuration database
    2560-03-27 22:38:42 <SCADA-PC><SYSTEM><ACT> The formulas source code has been compiled
    2560-03-27 22:38:42 <SCADA-PC><SYSTEM><ACT> Connection listener is started
    2560-03-27 22:38:42 <SCADA-PC><SYSTEM><ACT> Start server
    2560-03-27 22:38:42 <SCADA-PC><SYSTEM><ACT> Current data are loaded
    2560-03-27 22:38:50 <SCADA-PC><SYSTEM><ACT> Connect to client 127.0.0.1
    2560-03-27 22:38:50 <SCADA-PC><SYSTEM><ACT> The user ScadaComm is successfully authenticated
    2560-03-27 22:39:59 <SCADA-PC><SYSTEM><ACT> Connect to client 127.0.0.1
    2560-03-27 22:39:59 <SCADA-PC><SYSTEM><ACT> The user ScadaWeb is successfully authenticated
    2560-03-27 22:39:59 <SCADA-PC><SYSTEM><ACT> Check user admin name and password. Result: passed
    2560-03-27 22:42:35 <SCADA-PC><SYSTEM><ACT> Disconnect client 127.0.0.1
    2560-03-28 18:57:25 <SCADA-PC><SYSTEM><ACT> Connect to client 127.0.0.1
    2560-03-28 18:57:25 <SCADA-PC><SYSTEM><ACT> The user ScadaWeb is successfully authenticated
    2560-03-28 18:57:34 <SCADA-PC><SYSTEM><ACT> Check user admin name and password. Result: passed

    in reply to: Numbers can not be seen in the table. #2050
    phachakorn
    Participant

    hourly file

    in reply to: Numbers can not be seen in the table. #2044
    phachakorn
    Participant

    Hi Mikhail
    I checked It has a raw hourly data exist.
    But there is the inaccuracy of the number of years.
    Look at the picture.
    hourly data file
    data file

    Please how to fix

    thanks you

    • This reply was modified 7 years, 1 month ago by phachakorn.
    in reply to: Numbers can not be seen in the table. #2037
    phachakorn
    Participant

    Hi Mikhail
    Thanks for the quick answer.
    But my software has run for 48 hours ago.
    And now I have not seen any numbers in hour columns.
    Please how to fix

    thanks you