tom040264Participant
ScadaServerSvc.log:
2018-06-15 16:43:17 <HP-SERVER><SYSTEM><ACT> ScadaServerService 5.1.0.3 is started
2018-06-15 16:43:19 <HP-SERVER><SYSTEM><ACT> Check the existence of the data directories is completed successfully
2018-06-15 16:43:19 <HP-SERVER><SYSTEM><ACT> Check the existence of the configuration database files is completed successfully
2018-06-15 16:43:22 <HP-SERVER><SYSTEM><ACT> Input channels are read from the configuration database. Active channel count: 10
2018-06-15 16:43:22 <HP-SERVER><SYSTEM><ACT> Ouput channels are read from the configuration database
2018-06-15 16:43:22 <HP-SERVER><SYSTEM><ACT> Users are read from the configuration database
2018-06-15 16:43:22 <HP-SERVER><SYSTEM><ACT> Formulas are read from the configuration database
2018-06-15 16:43:23 <HP-SERVER><SYSTEM><ERR> Error compiling the source code of the formulas:
Line 523, column 55: error CS1501: Keine Überladung für die Methode ‘GetBit’ nimmt 1-Argumente an.
Line 526, column 55: error CS1501: Keine Überladung für die Methode ‘GetBit’ nimmt 1-Argumente an.
Line 529, column 56: error CS1501: Keine Überladung für die Methode ‘GetBit’ nimmt 1-Argumente an.
See the file C:\SCADA\ScadaServer\Log\CalcEngine.cs with the source code
2018-06-15 16:43:23 <HP-SERVER><SYSTEM><ERR> Normal program execution is impossible.
2018-06-15 18:44:08 <HP-SERVER><SYSTEM><ACT> ScadaServerService is stopped
——————————————————————————–
——————————————————————————–
2018-06-15 18:44:08 <HP-SERVER><SYSTEM><ACT> ScadaServerService 5.1.0.3 is started
2018-06-15 18:44:09 <HP-SERVER><SYSTEM><ACT> Check the existence of the data directories is completed successfully
2018-06-15 18:44:09 <HP-SERVER><SYSTEM><ACT> Check the existence of the configuration database files is completed successfully
2018-06-15 18:44:09 <HP-SERVER><SYSTEM><ACT> Input channels are read from the configuration database. Active channel count: 10
2018-06-15 18:44:09 <HP-SERVER><SYSTEM><ACT> Ouput channels are read from the configuration database
2018-06-15 18:44:09 <HP-SERVER><SYSTEM><ACT> Users are read from the configuration database
2018-06-15 18:44:09 <HP-SERVER><SYSTEM><ACT> Formulas are read from the configuration database
2018-06-15 18:44:09 <HP-SERVER><SYSTEM><ERR> Error compiling the source code of the formulas:
Line 523, column 56: error CS1501: Keine Überladung für die Methode ‘GetBit’ nimmt 1-Argumente an.
See the file C:\SCADA\ScadaServer\Log\CalcEngine.cs with the source code
2018-06-15 18:44:09 <HP-SERVER><SYSTEM><ERR> Normal program execution is impossible.ScadaWeb.log
2018-06-15 18:17:11 <HP-SERVER><DefaultAppPool><ACT> Initialize common web application data
2018-06-15 18:17:11 <HP-SERVER><DefaultAppPool><ACT> Connect to SCADA-Server “localhost”
2018-06-15 18:17:12 <HP-SERVER><DefaultAppPool><EXC> Error connecting to SCADA-Server: Es konnte keine Verbindung hergestellt werden, da der Zielcomputer die Verbindung verweigerte 127.0.0.1:10000
2018-06-15 18:17:12 <HP-SERVER><DefaultAppPool><ACT> Disconnect from SCADA-Server
2018-06-15 18:17:12 <HP-SERVER><DefaultAppPool><EXC> Error refreshing the tables of the configuration database:
Scada.ScadaException: Unable to receive the configuration database modification time.
bei Scada.Client.DataCache.RefreshBaseTables()
2018-06-15 18:17:12 <HP-SERVER><DefaultAppPool><ACT> User information has been added. IP address: 91.113.32.125. Session: fmn4stqwwpvgopgm52hkwfpw
2018-06-15 18:17:12 <HP-SERVER><DefaultAppPool><ERR> Unable to connect to SCADA-Server. Try again.
2018-06-15 18:17:12 <HP-SERVER><DefaultAppPool><ERR> Unsuccessful login attempt: admin – Server is unavailable. IP address: 91.113.32.125
2018-06-15 18:17:14 <HP-SERVER><DefaultAppPool><ERR> Unable to connect to SCADA-Server. Try again.
2018-06-15 18:17:14 <HP-SERVER><DefaultAppPool><ERR> Unsuccessful login attempt: admin – Server is unavailable. IP address: 91.113.32.125
2018-06-15 18:17:14 <HP-SERVER><DefaultAppPool><ERR> Unable to connect to SCADA-Server. Try again.
2018-06-15 18:17:14 <HP-SERVER><DefaultAppPool><ERR> Unsuccessful login attempt: admin – Server is unavailable. IP address: 91.113.32.125
2018-06-15 18:37:20 <HP-SERVER><DefaultAppPool><ACT> User information has been removed. IP address: 91.113.32.125. Session: fmn4stqwwpvgopgm52hkwfpw
2018-06-15 18:38:24 <HP-SERVER><DefaultAppPool><ACT> Connect to SCADA-Server “localhost”
2018-06-15 18:38:25 <HP-SERVER><DefaultAppPool><EXC> Error connecting to SCADA-Server: Es konnte keine Verbindung hergestellt werden, da der Zielcomputer die Verbindung verweigerte 127.0.0.1:10000
2018-06-15 18:38:25 <HP-SERVER><DefaultAppPool><ACT> Disconnect from SCADA-Server
2018-06-15 18:38:25 <HP-SERVER><DefaultAppPool><EXC> Error refreshing the tables of the configuration database:
Scada.ScadaException: Unable to receive the configuration database modification time.
bei Scada.Client.DataCache.RefreshBaseTables()
2018-06-15 18:38:25 <HP-SERVER><DefaultAppPool><ACT> User information has been added. IP address: 127.0.0.1. Session: 5h2nvzvuesmbbumghftk20vm
2018-06-15 18:38:33 <HP-SERVER><DefaultAppPool><ERR> Unable to connect to SCADA-Server. Try again.
2018-06-15 18:38:33 <HP-SERVER><DefaultAppPool><EXC> Error refreshing the tables of the configuration database:
Scada.ScadaException: Unable to receive the configuration database modification time.
bei Scada.Client.DataCache.RefreshBaseTables()
2018-06-15 18:38:33 <HP-SERVER><DefaultAppPool><ERR> Unable to connect to SCADA-Server. Try again.
2018-06-15 18:38:33 <HP-SERVER><DefaultAppPool><ERR> Unsuccessful login attempt: admin – Server is unavailable. IP address: 127.0.0.1“Unable to connect because the destination computer refused the connection 127.0.0.1:10000”
tom040264ParticipantHi,
I tried to solve the problem by using of this tread but without any successes. For 20 minutes everything worked perfect and I did some changes in the ComServer (I tried to add a command). Then I tried to load the SCADA-Page as usual, but I got the message “Server is unavailable.”
This is the WebSettings file:
<?xml version=”1.0″ encoding=”utf-8″?>
<WebSettings>
<CommSettings>
<Param name=”ServerHost” value=”localhost” descr=”SCADA-Server host or IP address” />
<Param name=”ServerPort” value=”10000″ descr=”SCADA-Server TCP port number” />
<Param name=”ServerUser” value=”ScadaWeb” descr=”User name for the connection” />
<Param name=”ServerPwd” value=”12345″ descr=”User password for the connection” />
<Param name=”ServerTimeout” value=”10000″ descr=”Response timeout, ms” />
</CommSettings>
<CommonParams>
<Param name=”Culture” value=”” descr=”Web application culture” />
<Param name=”DataRefrRate” value=”1000″ descr=”Current data and events refresh rate, ms” />
<Param name=”ArcRefrRate” value=”10000″ descr=”Archive data refresh rate, ms” />
<Param name=”DispEventCnt” value=”100″ descr=”Display events count” />
<Param name=”ChartGap” value=”90″ descr=”Distance between chart points to make a gap, sec” />
<Param name=”StartPage” value=”” descr=”Start page after login” />
<Param name=”CmdEnabled” value=”true” descr=”Enable commands” />
<Param name=”CmdPassword” value=”true” descr=”Require password to send command” />
<Param name=”RemEnabled” value=”true” descr=”Allow to remember logged on user” />
<Param name=”ViewsFromBase” value=”true” descr=”Load view settings from the database” />
<Param name=”ShareStats” value=”true” descr=”Share depersonalized stats with the developers” />
</CommonParams>
<ScriptPaths>
<Script name=”ChartScript” path=”~/plugins/ChartPro/js/chartdialog.js” />
<Script name=”CmdScript” path=”~/plugins/Table/js/cmddialog.js” />
<Script name=”EventAckScript” path=”~/plugins/Table/js/eventackdialog.js” />
</ScriptPaths>
<Plugins>
<Plugin fileName=”PlgChart.dll” />
<Plugin fileName=”PlgChartPro.dll” />
<Plugin fileName=”PlgConfig.dll” />
<Plugin fileName=”PlgRegistration.dll” />
<Plugin fileName=”PlgSchBasicComp.dll” />
<Plugin fileName=”PlgScheme.dll” />
<Plugin fileName=”PlgStore.dll” />
<Plugin fileName=”PlgTable.dll” />
<Plugin fileName=”PlgWebPage.dll” />
</Plugins>
</WebSettings>The CPU load of ScadaServerSvc.exe is 0.
Any idea?tom040264ParticipantHi Mikhail,
I have found the error. It was in my modem-router. The port 10000 was open, and redirected, but (I am an idiot!) the standard WebPort 80 has not been opened.
Thank you and sorry for this misunderstanding.
tom040264ParticipantHi Mikhail,
It is a very old tread, but unfortunately I am still not able to connect to SCADA from “outside” of my Network. In the meantime it is not possible to open the Image you posted a year ago.
What did I do? I opened a port 10000 on my router (Frizbox 3390) and rerouted it to the posrt 10000 on my SCADA Computer. On this computer I opened in firewall a port with the number 10000. Is this the right way?
Thx in advance
BR
T.tom040264ParticipantThe architecture is easy: a Win10 computer 24/7 as SCADA server, some Win10 or android clients. From each of them I can reach the server, but from the internet it is not possible. The router/ modem is a FritzBox 3390.
tom040264ParticipantIt seems as if it is a small misunderstanding. I understood, that Rapid SCADA has an integrated WEB-server, and the other computers hold the data from it.
I have no web server, neither i my home network, nor in the internet.
tom040264ParticipantHi,
The access from any computer within the home-network to the SCADA server works perfect, but how can I access the server from the internet? I’ve opened a port 10000 on the router/modem, and on the SCADA server (a new rule in the firewall). I have a static address (via dyndns). Then I tried with:
but it didn’t work. Is it enough just to open the port? Which application should I start behind this port.
Thank you!
BR
T.- This reply was modified 7 years, 7 months ago by tom040264.
tom040264ParticipantHi Mikhail,
You are fully right. This was the reason.
Thank you
T.December 3, 2016 at 9:59 am in reply to: Writing additional data (for example infotext) to historical DB #1801tom040264ParticipantHello Mikhail,
I have a “basic question” (there are no stupid questions): after I have connected the module ModDBExport.dll, which program can I use the SQL data base with? I have found the description in dbexport_en, but honestly speaking I don’t understand is it a mater of Administrator or Communicator.
Thank you in advance
T.tom040264ParticipantHello Mikhail,
The problem is, that there is not so much documentation in English regardin FS20, or I can not finde it. Here is a link to something what could give you the overview:
http://fhem.de/commandref.html#FS20
Another question: can Rapid SCADA read something from a text file and visualise it as a text variable? I haven’t fine anything about this in the documentation or in this forum.
BR
T.tom040264ParticipantThank you Mikhail, it works!
The modbus device is connected. The next step is to connect the FS20 system from contronics, but I have absolutely no idea where to start.
Br
T.tom040264ParticipantHello Sergey,
Can you help me plese? I have the same problem and cann’t finde the way to display any charts or pictures.
BR
T.tom040264ParticipantHello,
First of all thank you for the quick response. This is clear, but how can I get to the Web configuration mask/form like in the User Manual described? I have found no way there.
T.
tom040264ParticipantHello Mikhail,
I did login the Webstation app as administrator, went to Main Menu > Configuration > Web application, but I was able to see only the status of different plugins (Active) and had the possibility to deactivate them.
How can I start any of these plugins, e.g. Web Configurator?
Thank you in advance
T. -