MikhailModeratorLikely port 502 is required.
MikhailModeratorRapid SCADA 6.4.6 has been released.
Upgrade new mimics:
– Supports custom CSS and JS
– Text component supports conditions for selecting text
– Scripts of child faceplate components are executed
– Custom scripts are executed in edit mode
– Exported faceplate properties can be linked to mimic document properties
– Exported faceplate properties contain default bindings
MikhailModeratorHi,
According to the communication line log you can successfully connect to the device by IP, but it is not responding.
I suppose the device ID (unit ID) is wrong as written above. Most common are 0 and 1.
Use https://rapidscada.net/modbus/ to decode data packets. It is useful for understanding.
MikhailModeratorHi,
You could find and replace the file. Is is in the ScadaWeb folder.
Also try Notifocation Plugin.
MikhailModerator1. I suggest to set the channel’s archive mask to an empty value. In that case, channel values will be written in the default archives.
2. Upload the HelloWorld project for execution and make sure that it writes hourly values.
3. Check ScadaServer.log and ScadaServer.txt for errors and additional info.
-
This reply was modified 1 month, 4 weeks ago by
Mikhail.
MikhailModeratorHello,
Please clarify your question by providing screenshots.
MikhailModeratorHello,
The Server scripting engine has no references to the MQTT classes.
What is the general idea of ​​how the script should work?
I suggest this manual about Server scripts https://rapidscada.net/docs/en/latest/configuration/scripts
MikhailModeratorHi,
This is a known bug. It will be fixed in the next release.
MikhailModeratorI’m glad everything worked 🙂
MikhailModeratorIf you want all channels to be written in the custom archive, set the Is Default field for the archive.
MikhailModeratorHi,
Let’s make the custom archive work!
Note that you should add a custom archive with the same Code to the Server settings, and to the Archives table in the configuration database.
If this has already been done, please send screenshots of the relevant settings.March 27, 2026 at 11:13 am in reply to: Will the content of the custom event be recorded in the text field? #17799
MikhailModeratorHello,
Please provide more details and screenshots.
MikhailModeratorHi,
A variation on the same idea:
1. Deploy a separate instance of the web application for mobile users.
2. Add views for mobile in a different folder.
3. Set a corresponding start view for mobile users in the web app settings.
MikhailModeratorHello,
It looks like something wrong with the web application. If you start the Scada website in the IIS management console, what happens next? -