  • in reply to: OPC Server in RapidSCADA #1341
    Mikhail
    Moderator
    in reply to: Communication is not established with MODBUS simulator #1340
    Mikhail
    Moderator

    OK 🙂

    in reply to: Signal Number ? #1339
    Mikhail
    Moderator

    Hi,
    To publish an image you need external hosting, e.g. postimage.org
    Could you provide more information about your questions?

    in reply to: Communication is not established with MODBUS simulator #1331
    Mikhail
    Moderator

    Use postimage.org and post links.

    in reply to: Communication is not established with MODBUS simulator #1329
    Mikhail
    Moderator

    Post screenshots for such questions, please.

    in reply to: Communication is not established with MODBUS simulator #1327
    Mikhail
    Moderator

    Probably the Simulator doesn’t support more than 1 connection.
    You can set another TCP port followed by IP address: 127.0.0.1:503

    in reply to: Error in TCP modbus simulation #1326
    Mikhail
    Moderator

    The formula is applied in SCADA-Server. That’s why you can’t see a result in Communicator. You have to configure displaying data by SCADA-Web app and you will be able to see calculation results.

    in reply to: Communication is not established with MODBUS simulator #1321
    Mikhail
    Moderator

    Do the both communications the old and the new work in parallel?
    Post a piece of communication log, please.

    in reply to: Error in TCP modbus simulation #1319
    Mikhail
    Moderator

    You should use a formula of the appropriate input channel in SCADA-Administrator application.

    The formula below will be useful. Add it in the Formulas table and use in the formula of the input channel.

    public double GetByte(double val, int n)
    {
        UInt64 uintVal = (UInt64)val;
        return (uintVal >> (n*8)) & 0xFF;
    }
    

    The formula of the input channel is like

    (((256*GetByte(Cnl,3))+GetByte(Cnl,2))+(GetByte(Cnl,1)/256)+(GetByte(Cnl,0)/(256*256)))/10
    

    I haven’t tested it.

    in reply to: Communication is not established with MODBUS simulator #1318
    Mikhail
    Moderator

    Hi,

    Mudbus TCP usually uses 502 port. Try setting up the communication channel. Use TCP client channel type.

    in reply to: Error in TCP modbus simulation #1314
    Mikhail
    Moderator

    If you’d like to switch off SCADA-Server, you should uncheck Use SCADA-Server option in Communicator.

    in reply to: Error in TCP modbus simulation #1313
    Mikhail
    Moderator

    You are requesting the same when the communication is OK and when it’s broken.
    It means that something wrong with a simulator application. May be some settings of the simulator were changed, e.g. device address.

    in reply to: request sequensce confusion #1312
    Mikhail
    Moderator

    active and bound option again in request sequence, while it is already taken in line parameter.

    Unchecking Active disables a whole communication line or a device.
    If Bound is true the data from a communication line or from a device are sent to the SCADA-Server. Unchecking Bound of a communication line is the same as unchecking this parameter of each device.

    significance of timeout and delay

    Timeout is the time while you are waiting for the responce from your device.
    Delay is the delay after receiving data before the next request.
    They should be set experimentally to provide stable communication.

    delay after request cycle

    Additional delay after requesting all the devices of the communication line.

    in reply to: OPC Server in RapidSCADA #1308
    Mikhail
    Moderator

    Hello,
    For now Rapid SCADA works as OPC client, not as OPC server.
    May be you can use DB, such as MySQL, for the integration purpose?

    in reply to: Does RapidScada Support HTTPS #1306
    Mikhail
    Moderator

    Hi,

    Yes. HTTPS is supported and configured by IIS. You should read about using certificates in the Internet.

    To enable HTTPS in Rapid SCADA, find all the web.config files in C:\SCADA\ScadaWeb and look for the commented blocks by the word “https”. You should uncomment them.