manjey73ParticipantUnfortunately, not yet, I suggested to Mikhail to add such an opportunity, since it was asked about back on version 5
October 22, 2024 at 8:47 am in reply to: Rapid SCADA 6.3.1 Installation, TCP port 10002 already in use. #15541
manjey73ParticipantChange the ScadaAgent port to another one other than 10002
<?xml version="1.0" encoding="utf-8" ?> <ScadaAgentConfig> <ListenerOptions> <Port>10002</Port>See the configuration file in the ScadaAgent\Config folder. After that, restart the services.
Also, when configuring the configuration, specify this port in the project Instances-
This reply was modified 1 year, 6 months ago by
manjey73.
manjey73ParticipantWith the Date and Time format, it is transmitted as a string, Cmd is not suitable here
Input Script –
Val()
Output Script –GetStrDt(CmdDataStr)orGetStrDtToUtc(CmdDataStr)Script Table
For Locale Timepublic double GetStrDt(string dt) { SetVal(CnlNum, EncodeDate(DateTime.Parse(dt))); return EncodeDate(DateTime.Parse(dt)); }For UTC Time
public double GetStrDtToUtc(string dt) { SetVal(CnlNum, EncodeDate(DateTime.Parse(dt).ToUniversalTime())); return EncodeDate(DateTime.Parse(dt).ToUniversalTime()); }
manjey73ParticipantIn a simple version, you can control it through the start variable
In this case, the PLC does not actually stop, it does the work of “Doing nothing”if (start) { Your program } else do nothing
manjey73ParticipantIt seemed to me that the start and stop of the PLC is not related to the protocol, it is a higher level.
But it can also be solved through protocol variables, but for this your PLC program must be written accordingly. These are fundamentally different approaches.October 15, 2024 at 8:27 am in reply to: Seeking Guidance on Rapid SCADA Configuration for Real-Time Monitoring #15518
manjey73ParticipantData Acquisition: How do I connect my PLC to Rapid SCADA: ?? Are there specific drivers or protocols I should be aware of: ??
What kind of PLC do you have?
Does it support the Modbus protocol?Visualization: I want to create user friendly dashboards. What are the best pracices for designing visualizations in Rapid SCADA:?? Any tips on using the built-in components effectively: ??
What exactly do you want to draw?
There are video tutorials on Yutube
September 14, 2024 at 12:07 pm in reply to: How to retrieve data from the Channels table in a custom module? #15457
manjey73ParticipantCnl CnlArc = ServerContext.Cnls.ArcCnls.Values.Where(x => x.CnlNum == cnlNum).FirstOrDefault();It is possible to get from the Scada Module in this way through the required channels.
where is CnlNum the channel number you needThere are 4 types of channel lists
ArcCnls – all channels that can be saved in the database
CnlOut – output channels only
Calculated and another one where the input channels are// Каналы Archive - все Input, InputOutput, Calculated, CalculatedOutput try { Cnl CnlArc = ServerContext.Cnls.ArcCnls.Values.Where(x => x.CnlNum == cnlNum).FirstOrDefault(); if (CnlArc != null) { if (!dictCnl.ContainsKey(Name)) // Сразу добавлять в словарь наверное не получится, так как неизвестен поток ??? Известна программа { dictCnl.Add(Name, CnlArc); } } } catch { moduleLog.WriteLine($"НЕТ ArcCnls"); // TEST } // Каналы Output try { Cnl CnlOut = ServerContext.Cnls.OutCnls.Values.Where(x => x.CnlNum == cnlNum).FirstOrDefault(); if (CnlOut != null) { if (!dictCnl.ContainsKey(Name)) { dictCnl.Add(Name, CnlOut); } } } catch { moduleLog.WriteLine($"НЕТ OutCnls"); // TEST } }So I add the channels I need to my dictionaries as an example.
Next, you can study Cnl CnlArc and take the necessary actions depending on the Data Types, format, etc.
-
This reply was modified 1 year, 7 months ago by
manjey73.
manjey73ParticipantThis is a test of the second formula.
You need to create 8 calculation channels and specify in the formula which channel to take data from and which byte to take.
GetByte1(105, 6) is an example to take the 6th byte. The value can be from 0 to 7
manjey73Participant
manjey73Participantpublic double GetByte1(int num, int bytenum) { byte[] mass = BitConverter.GetBytes(Val(num)); if (bytenum >= 0 && bytenum <= 7) { return Convert.ToDouble(mass[bytenum]); } else return double.NaN; }This formula will probably be more correct with your values
manjey73Participantpublic double GetByte(double val, int n) { UInt64 uintVal = (UInt64)val; return (uintVal >> (n * 8)) & 0xFF; }I’m not sure if this will work correctly. I’ll try to check in VisualStudio
manjey73ParticipantWell, do you want exactly what I assumed?
manjey73ParticipantI did not try to check the channel type from the driver immediately before recording, for example, if I created an integer channel directly by the driver, and the user then changed it to double.
If there is such an opportunity, then it is very good.
manjey73ParticipantDo you want to have 8 channels with a number display 111, 114, 98, 111, 108, 108, 101 and 72 ?
5th version does not support arrays. You will have to get everything into the input channel in double, then make 8 calculation channels and write a script that will pull out the required from the total “number” either in the form of strings or in the form of numbers.
manjey73ParticipantYou can assign the channel data type directly in the driver. Including in the View, you also generate code that allows you to use the Channel Creation Wizard based on your driver’s code. That is, the user does not need to think about what type of channel needs to be set for the signal, the channel creation wizard will do everything necessary.
I don’t remember if it is possible to check channel types from the driver code, since it is configured even before you create channels, but it can definitely help create channels and even specify the required formulas. For example, look at the Modbus code when setting up the bitmask.
-