Viewing 15 posts - 91 through 105 (of 981 total)
  • in reply to: Evento de perda de comunicação – Rapid SCADA 6.2.2 #17665
    There is a Status service tag for devices in the Communicator. This is probably the best solution.
    in reply to: Multipule tags chart #17648
    Use ChartPro
    in reply to: I can’t open or Edit Mimic Files. #17646
    Use temporary keys for Mimic on the Windows development computer and that’s it. Then, when you commit the project to a Linux server where the keys are permanent, everything will work.
    In the Format table, add an enumeration for your values, for example 0=Stop, 1=Start, etc.
    Stop; Start; Pause; Manual
    Then turn on the script execution in the channel and add your enumeration to the format.
    This will be a pop-up command window with 4 buttons.
    If you want to draw 4 separate buttons, then you probably have to act differently. For example, make 4 separate output channels for one command tag code and write the required value in each output formula, and indicate “Send command immediately” on the mnemonic
    in reply to: Backup strategy for distributed system #17572
    on local systems, you can use rapidgate, it allows you to synchronize data like. as well as perform the download on command.
    in reply to: Scada webstation not getting open #17569
    The scada core itself is free and open source. There have always been paid components that you can do without, except in some cases.
    someone installed dancing and tambourine on Winows 7. but in general, yes, it’s better to use Windows 10 or 11.
    in reply to: Dynamic text- forbid/ allow the writing/ input #17559
    You can send a Double.NaN in cases where the command should not pass, or cause an exception in the command with the message that commands are failed only in manual mode.
    In that case CsvImport.exe can help
    With your hands ?
    As far as I understand, there is channel A and channel B and channel C, which is calculated between A and B. Channels A and B have the option to download again.
    How can I restore channel C by pressing one button?
    How do you enter the data manually?
    Scripts do not work with historical data. Most likely, you will need some kind of module that, after filling in the data, will perform the same calculation but fill in the data in the past time.
    in reply to: Input Chanel Size and string format #17512
    DataType = UnicodeString
    Format – String
    InputScript = SplitUnicode(()=> "10-PME-01")
    The string must be divided by the channels of the array
    in reply to: Input Chanel Size and string format #17508
    In version 6, it is now possible to combine channels into an array. To do this, specify the length of the data in the channel table.
    An example of text notes.
    Note
    in reply to: Required to write a formula for a command #17476
    Then you need a little more configuration data.
    including screenshots and which schema editor do you use?
    in reply to: Required to write a formula for a command #17473
    In the output formula, something like
    Val() > 0 ? 0: 1
    in reply to: Universal / pre-made / generic popup like motor #17449
    In the new Mimic editor, there is such a thing as Faceplate. But that’s exactly what requires some intervention from the developer so that you can make these faceplates so that others can use them. So far, the main problem in them, as it seems to me, is channel binding, since different people can call the same things in different languages (for example, the tag code).
    Well, there’s also a whole list 🙂