  • in reply to: Where is Administration Application #14563
    Mikhail
    Moderator

    In addition, this video shows how to connect from the Administrator app, which is installed on Windows, to a Linux instance of Rapid SCADA.

    in reply to: OPC UA client connection setup ? #14562
    Mikhail
    Moderator

    That article is about configuring OPC Classic for Rapid SCADA 5.

    > What about the timeout, delay, time, period, string address or host name, name ?
    Time and period do not work. Address is ignored. Delay is used internally. I recommend to use the default values.

    > Also on the TagName thing, for the first time, I need to join two OPCUA string values together.
    It would be easier if you get a string in a one OPC UA tag instead of joining channels. Concatenation of string channels is possible, but the formula may be tricky.

    in reply to: Comparing two values with using formula #14545
    Mikhail
    Moderator

    Hello,
    You need to add a new channel of the calculated type with a formula
    Val(101) > Val(102) ? 1 : 0
    where 101 and 102 the channels to compare.
    Then use Automatic Control Module to send command according to the value of the added channel.

    If you have questions during the implementation of the above solution, send screenshots of your settings.

    Mikhail
    Moderator

    Hi,

    You don’t need to disable firewall. You need to configure it. Allow incoming connections to the TCP port in use.

    Please use different topics for different questions. Discussion about scheme components should be in other thread.

    Mikhail
    Moderator

    Hi,
    There is no software limits. However, if you have many connections, you should test if the network is good enough for that.

    in reply to: V6 ModDbExport for historical data #14541
    Mikhail
    Moderator

    Hi,

    Yes, you can use archive replication for this purpose.
    Command example for database export

    cmd=ExportArchive
    startDT=2022-12-23 10:00:00
    endDT=2022-12-23 11:00:00
    
    in reply to: Modbus Data Formula #14539
    Mikhail
    Moderator

    Note that the above works in Rapid SCADA 6.

    in reply to: Chart not Displaying Data #14528
    Mikhail
    Moderator

    🙂

    in reply to: Modbus TCP Server #14526
    Mikhail
    Moderator

    According to the log, TCP server is waiting for incoming connections, but no client is trying to connect.
    Is Rapid SCADA installed on a cloud server or in the local network?

    in reply to: Chart not Displaying Data #14521
    Mikhail
    Moderator

    Make sure that you copied PlgChartPro.xml and PlgChartPro_Config.xml into the project.

    in reply to: Modbus TCP Server #14520
    Mikhail
    Moderator

    Also try to connect to Communicator by any TCP client utility. You should see that a connection is established.

    in reply to: Modbus TCP Server #14519
    Mikhail
    Moderator

    Hello Ibrahim,

    Please provide screenshots of the Communicator settings and the communication line log.

    Make sure that the modems are configured to initiate a connection to the TCP server.

    in reply to: Chart not Displaying Data #14516
    Mikhail
    Moderator

    I recommend to upgrade Rapid SCADA to the latest version.

    in reply to: How to extract MQTT message completely #14513
    Mikhail
    Moderator

    Thank you.

    Mikhail
    Moderator

    Device status is available. Each device in Communicator contains a hidden tag with the code Status
    If you create a channel, specify the device and tag code (Status), the device status will be received in this channel. 0 – normal, 1 – error

    Line status currently cannot be received by a channel. To implement this, there should be a channel number in the line options. But it looks ugly. We should find a better idea.