  • in reply to: Modbus to Rapid Scada to PLC #14976
    Mikhail
    Moderator

    Hello,

    More info needed.
    Are those 3 PLCs operate as Modbus master (client) or Modbus slave (server)?

    in reply to: automatic restart communication line #14975
    Mikhail
    Moderator

    The OPC UA server that is built in Communicator cannot send commands to the application. You should look for another way of sending commands to Rapid SCADA. May be, via a database or 3rd party OPC server.

    in reply to: bflat native instead of runtime ? #14973
    Mikhail
    Moderator

    Hi,
    Do you mean to include .NET inside Rapid SCADA executables?

    in reply to: reference lines of Chart Pro #14972
    Mikhail
    Moderator

    Create 2 channels of the Calculated/Output type in the Channels table.
    Specify their numbers in the Limits table in a limit row.
    Display the created channels in a table view.
    Then provide screenshots.

    in reply to: Above value result zero #14971
    Mikhail
    Moderator

    Could you provide screenshots of the settings and error?

    in reply to: DbImport MSSQL #14970
    Mikhail
    Moderator

    🙂

    in reply to: RapidScada Windows 11 on ARM #14969
    Mikhail
    Moderator

    Hello,

    I’m not sure that it can work on Windows ARM.
    If the Rapid SCADA services work, check log files ScadaServer.log, ScadaComm.log and ScadaWeb.log

    in reply to: reference lines of Chart Pro #14950
    Mikhail
    Moderator

    In this case, create 2 extra channels, max and min. Set them as limits of the 1st channel (see this page). To display them on a chart, you need to select them manually or display chart as a view with predefined channels.

    in reply to: automatic restart communication line #14949
    Mikhail
    Moderator

    Do you mean that you need to restart a line by another OPC UA client?
    If so, you need a channel that can be changed by the client, and use Automatic Control Module to send a command depending on that channel.

    in reply to: Above value result zero #14948
    Mikhail
    Moderator

    Hello,
    Channel formula example,
    Cnl <= 10 ? Cnl : 0
    Condition ? expression1 : expression2

    in reply to: DbImport MSSQL #14947
    Mikhail
    Moderator

    Current driver version supports number values. We will support 4 char strings in the next driver version.

    in reply to: DbImport MSSQL #14946
    Mikhail
    Moderator

    Hi,
    You have to fill the tags in the device properties. One tag per line

    in reply to: Multiple Y-axes #14940
    Mikhail
    Moderator

    > I just want to know how many Y axes can be used at most
    There is no software limit. If you create too many axes, they will appear ugly, I suppose.

    in reply to: automatic restart communication line #14939
    Mikhail
    Moderator

    Create a channel of the Output type and set Tag Code to the above.

    in reply to: automatic restart communication line #14938
    Mikhail
    Moderator

    Hi,
    In version 6 you can send a command to restart a line.
    Supported commands are here.
    Command value is a line number to restart.