  • in reply to: Primary/backup redundancy in v6: failover behavior #18607
    Mikhail
    Moderator

    > what is the recommended way in 6 to switch polling between the two Communicators, manually or by time? Is it done by enabling/disabling communication lines by command, or another mechanism?

    It is done by Start/Stop commands to communication lines.
    First, try configuring manual commands. Then you can use Replication Helper to send them automatically.

    Rapid Gate can be configured to sync data either manually or automatically.

    > which Communicator setting is used to send data to several Servers?

    In the Data Sources section, add a new data source with the DrvDsScadaServer driver.

    > also gladly accept the example configuration for Automatic Poll Switching

    Please send a request to info@…org

    > With your permission, we would like to summarize the four strategies from your document in the community companion we are writing, with credit and a link to this thread.

    OK.

    in reply to: Primary/backup redundancy in v6: failover behavior #18603
    Mikhail
    Moderator

    > Failover: Is there any built-in failover in v6? Can Communicator and Webstation be configured with a backup Server connection and switch automatically?
    Communicator can send data to several servers. Automatic switching is implemented by using Rapid Gate and Replication Helper.

    > Or is switchover expected to be handled outside Rapid SCADA (virtual IP, DNS, manual)?
    To backup the web application, a 3rd party balancer is used in some implementation.

    > Recommended architecture: For primary/backup, do you recommend two complete instances (Server + Communicator + Webstation on each computer, both Communicators polling), or one active Communicator feeding both Servers?
    My favorite is 2 different intendent instances because is clear and simple. Each includes Server, Communicator and Webstation.

    > Rapid Gate in primary/backup mode:
    Should gateways be configured in both directions (A→B and B→A)?
    If both Communicators poll the devices, should current data still be forwarded, or only events, acknowledgements and archives?
    If Rapid Gate is used to sync data, only one Communicator should work at a moment.

    > The v5 docs mention that forwarded values may have their formulas applied twice on the target. Does that still apply in v6?
    In v6, it is solved by Rapid Gate options.

    > Event acknowledgement: What is the recommended way to keep acknowledgements consistent on both servers?
    There is a server option to generate a special command when an event is ack’ed. Such commands are transferred by Rapid Gate to sync acks.

    > Licensing: Is one Rapid Gate license needed per Server in a primary/backup pair?
    Rapid Gate is needed on the main server.
    Replication Helper is needed on the main and backup server.

    As a recap, Rapid SCADA supports various redundancy options. In my view, you should choose the simplest option that meets your needs. Of course, if you require the most comprehensive solution, then go with that one.

    in reply to: Primary/backup redundancy in v6: failover behavior #18602
    Mikhail
    Moderator

    Hello,

    Based on this document:
    In Modbus TCP is used, the most simple method is polling a device by the main and backup Rapid SCADA instances in parallel independently. But data in archives might be slightly different.
    In addition, each instance can write a few copies of data. For example, write files and write to PostgreSQL database.

    If you need the archives to be synchronized, it is described by “Automatic Poll Switching” at page 4. Two software modules work together: Rapid Gate and Replication Helper. The last one is included in Rapid SCADA Enterprise. This combination is somewhat complex to set up. If you’d like to give it a try, I can send you an example.

    • This reply was modified 2 days, 1 hour ago by Mikhail.
    • This reply was modified 2 days, 1 hour ago by Mikhail.
    in reply to: [Release] Communication Drivers Collection for Rapid SCADA v6.0 #18599
    Mikhail
    Moderator

    Hi,
    I’ve checked that the links to GitHub in the Store are valid for the new version.

    in reply to: Question regarding Rapid SCADA Embedded License #18597
    Mikhail
    Moderator

    Hello,

    The Embedded edition is intended for single-board computers and controllers such as Raspberry Pi, Advantech MIO-2363, Moxa.

    For a VM on Synology RS820, regular licenses are needed.

    in reply to: Input Channel In Scripting #18594
    Mikhail
    Moderator

    Hi,

    For example, When trying to see Pump A data, just click Pump A Button, Same for Pump B, etc..

    Thank you for the explanation. Mimics are not designed for this scenario. It would be preferable to create a faceplate and put 3 faceplate instances on a mimic diagram. Or create 3 different mimic diagrams.

    in reply to: Input Channel In Scripting #18589
    Mikhail
    Moderator

    Perhaps, no.
    Could you explain, in general, why you need that?

    in reply to: Input Channel In Scripting #18587
    Mikhail
    Moderator

    Hello,
    Updating channel number does not work, because binding is performed when a mimic is loaded. It should be possible to change other component properties (i.e. colors) on button click.

    in reply to: New release Rapid SCADA 6.5.x #18584
    Mikhail
    Moderator

    Rapid SCADA 6.5.1 has been released.
    – A new SMS Parser driver has been added to the distribution.
    – Fixed bugs in other drivers.
    – Fixed bugs in Mimic Editor.

    in reply to: Chart Pro Plugin – Possible to annotated Min and Max Value? #18580
    Mikhail
    Moderator

    Hi,

    At the moment, Chart Pro does not have this option. Let me add it to the backlog.

    in reply to: PlgMimSVGAnimationJP #18574
    Mikhail
    Moderator
    in reply to: Inaccuracy in the Rapid SCADA Documentation #18570
    Mikhail
    Moderator

    Hello,
    Thank you for noticing.
    The Channel.Code field used to be informational. However, now it is used by mimics.
    The documentation should be fixed.

    in reply to: OPCUA Server Certificate Period #18566
    Mikhail
    Moderator

    4. Still got 1 year certificate

    Is it generated with a new expiration date or the same?

    in reply to: OPCUA Server Certificate Period #18565
    Mikhail
    Moderator

    The old driver stored certificates in some odd Windows storage. It was difficult to remove them.

    Please check if there are
    C:\Program Files\SCADA\ScadaComm\Config\DrvOpcUa.View.xml
    C:\Program Files\SCADA\ScadaComm\Config\DrvOpcUa.Logic.xml
    files?

    If so, remove then from the project and from the runtime directory. They contain some outdated setting where to store certificates.

    in reply to: OPCUA Server Certificate Period #18563
    Mikhail
    Moderator

    Hi,
    DrvOpcUa 6.1.2.0 (February 27, 2026) is up to date.
    Is there a chance that the existing certificate was created by the earlier version of the driver?
    Try deleting it, so the driver will create a new one.