Forum Replies Created
-
AuthorPosts
-
Thov
ParticipantAlright, it seems things have been solved:
I used your linked site and input the request first from Rapid Scada (00 01 00 01 00 10 6D D7) and got this:
00 Slave address 0x00 (0)
01 Function code 0x01 (1) – Read Coils
00 01 Starting address Physical: 0x0001 (1)
Logical: 0x0002 (2)
00 10 Quantity 0x0010 (16)
6D D7 CRC 0x6DD7 (28119)Then I did the same for a working coil request from Simply Modbus Master (01 01 00 00 00 10 3D C6) and got this:
01 Slave address 0x01 (1)
01 Function code 0x01 (1) – Read Coils
00 00 Starting address Physical: 0x0000 (0)
Logical: 0x0001 (1)
00 10 Quantity 0x0010 (16)
3D C6 CRC 0x3DC6 (15814)So the slave address was mismatching. I then went to Configurator Database -> Devices and set the address of the masterboard to 1:
https://imgur.com/gallery/p35RlR9I then reuploaded, and got successful data from masterboard (device nr. 1)!
https://imgur.com/gallery/IYeezmeThen I did the same as the previous step for the other two devices (device nr. 2 and 3), i.e. Configurator Database -> Devices and set their addresses to 1 as well. BUT: I left their Call numbers as 127.0.0.1. Remember that I set the Call number for device nr. 1 to blank as per your request at 2:06pm.
Then I set them to be active again in Instances -> Default -> Communicator -> Communication lines -> Line 1 parameters:
https://imgur.com/gallery/Rw9A1qPThen I reuploaded, and now I have all data coming from my devices, so we’re back in business 🙂
For the record, I don’t yet know precisely what I did wrong the first time or why it did not work, but I see that the addresses need to match, obviously – you probably have a better idea about why.
Thov
ParticipantDone, but no change. The device still outputs that it receives the requests from Rapid Scada as before.
Line 1 parameters:
https://imgur.com/gallery/lpEA0kSDevices:
https://imgur.com/gallery/dBnIxdRLine 1 stats:
https://imgur.com/gallery/ilVwN3uThov
ParticipantHi,
I hope these are the device properties you requested:
https://imgur.com/gallery/pxFga5tI use Modbus RTU via COM-port.
Thov
ParticipantI can also add that the device debugger prints request info when Rapid Scada requests data from it, as seen in the lines “RegCoilCB rd: 1, N …” :
https://imgur.com/gallery/YM63sYi -