Setting up events
Forum Home › Forums › Understanding the Software › Setting up events
Viewing 14 posts - 1 through 14 (of 14 total)
  • #18199
    oley
    I’m trying to define the most reasonable configuration of events for the channels.
    I have a few observations from my attempts so far.
    I already have about 20 objects in the system, each of which operates on over 200 channels. When a device restarts, or when communication is lost and then restored, I receive a flood of “Defined” events, which fill up the entire events window in the app and prevent me from going back to other events. How can I disable this type of event?
    Even without this behavior, the event window only displays the last 100 events, which is often insufficient. Question: Is there a way to reconfigure this and increase that number?
    What exactly is the difference between “channel data” and “channel value” has changed?
    #18200
    Channel data – value or status
    <Option name=”EventCount” value=”100″ />
    in ScadaWebConfig.xml
    #18201
    oley
    thank you.
    Is it possible to trigger an event only for selected status values?
    Am I correct in understanding that enabling “channel data has changed” has exactly the same effect as enabling both “channel value has changed” and “channel status has changed” together?
    #18202
    Yes, you can only enable “Status changed”
    and, depending on the destination, use monitoring and status change in the second part of the input formula.
    Channel formula : status formula
    #18203
    For example, you get a value from the Communicator that needs to be handled differently from the channel boundaries. The status in the normal state will always be =1, you use control based on other criteria and change the status to your own, respectively, adjust the status mask for displaying and controlling output to Events.
    #18204
    oley
    Thanks, could you give a simple example of this status formula?
    For example: I’m setting up an event for the channel as “status has changed”, but I only want to log it when status == Error (id=23).
    #18205
    Then you will most likely need settlement channels. Because otherwise you will register all statuses, not only =23. As far as I understand, events do not have filtration
    #18206
    That is, in the billing channel, you will always have either status 1 or 23, for example, and there will be fewer events.
    #18207
    If the “Channel is undefined” checkbox is not set in the channel’s event filter, I expect that such Defined/Undefined events should not be generated. Could you check please?
    #18208
    oley
    it happened for channels with “Channel status has changed” bit set.
    For all those channels after connection break I see in events table:
    27/07/2026 11:31:33 EFO CHOCIMINO EFO CHOCIMINO inverter #9 Temperatura wewnętrzna Defined, 33.600 °C
    I will disable this event.
    #18209
    It doesn’t seem to be treated, I also wondered about disabling (Normalization) when outputting Events.
    #18210
    As far as I remember, @Mikhail ‘s suggestion was to write in Postgre and filter at the DB level
    • This reply was modified 2 months, 1 week ago by manjey73.
    #18212
    Generating events is implemented here
    Please provide a screenshot of the channel event mask that causes unnecessary events.
    #18213