OPC Ua error

Tagged: 

Viewing 6 posts - 1 through 6 (of 6 total)
  • Author
    Posts
  • #12757
    quintelosky
    Participant

    Hi

    I’m using opc ua driver and I can connect to s7-1500 via opc, but I have an error when I try to connect to other opc ua server.

    I can use prosys opc ua browser but rapidscada can’t connect. Is anonymous , security mode and policy is none.

    https://ibb.co/0q4tHqc

    What can I do?

    Thanks

    #12758
    quintelosky
    Participant

    Hi

    I solved it.

    In “…\Instances\Default\ScadaComm\Config\DrvOpcUa.View.xml”

    Change:
    <!– WARNING: SHA1 signed certficates are by default rejected and should be phased out.–>
    <RejectSHA1SignedCertificates>false</RejectSHA1SignedCertificates>
    <MinimumCertificateKeySize>1024</MinimumCertificateKeySize>

    Now works fine

    Thanks

    #12763
    Mikhail
    Moderator

    Hi,

    Thank you for the update.
    Note that DrvOpcUa.View.xml affects user interface. DrvOpcUa.Logic.xml affects how the driver works.

    #12766
    quintelosky
    Participant

    Hi

    Yes, but I found a problem

    DrvOpcUa.Logic.xml is overwritten with default values, and the error continues.

    If I edit drvopcua.logic, communication works fine. But, when I upload a new configuration, I lost communication and I need edit the file.

    How can I do to mantain in DrvOpcUa.Logic.xml the new changes? (I put only-read attribute but I have an error when upload a new configuration)

    Thanks

    #12767
    manjey73
    Participant

    Transfer this file to your project folder

    #12768
    quintelosky
    Participant

    Many thanks

    Works fine