Modbus input channel scaling

Forum Home Forums Communicating with Devices Modbus Modbus input channel scaling

Viewing 3 posts - 1 through 3 (of 3 total)
  • Author
    Posts
  • #5039
    Derliin
    Participant

    Hei!

    I just started experimenting with Rapid Scada.
    I have set up modbus communication with a heating controller.
    How can I set scale factors for input channels?

    For example my device returns outdoor temp as -70.0 while its real value is -7.0.
    Thanks in advance!
    Aleksander.

    #5047
    Mikhail
    Moderator

    Hi,

    Open Administrator, find the appropriate input channel and set its formula, for example, Cnl/10

    #5048
    Mikhail
    Moderator