Minimum Sampling Rate on Scada in Server room table

Forum Home Forums Understanding the Software Minimum Sampling Rate on Scada in Server room table

Viewing 4 posts - 1 through 4 (of 4 total)
  • Author
    Posts
  • #5408
    slmhlm
    Participant

    Can we monitor the values in server room table with sampling rate less than 1 minute?
    It can not detect my alarm condition immediately. It detects only in every cross to new minute.

    I have found in the forum this answer from Mikhail:
    ”As a workaround you can manually set the value in C:\SCADA\ScadaServer\Config\ScadaServerSvcConfig.xml

    It defines how often snapshots are stored in minute data file. SCADA-Server shell may display custom values incorrectly despite of that it works.
    If you write more details about your task I could give more efficient advice.”

    • This topic was modified 4 years, 10 months ago by slmhlm.
    #5411
    Mikhail
    Moderator

    It can not detect my alarm condition immediately.

    You can, but it’s better to tick “Write events” and “Event on change” checkboxes of the input channel. And you will get events in case of alarms.

    #5412
    slmhlm
    Participant

    Thank you Mr. Mikhail.
    What about the refreshing trend graph lines in server room table less than 1 minute?

    • This reply was modified 4 years, 10 months ago by slmhlm.
    #5416
    Mikhail
    Moderator

    If you need to update chart plugin according to the custom requirements, we could discuss cost and deadline. In this case please contuct us by email and provide the detailed requirements.