Initial setup issues

Forum Home Forums Communicating with Devices Initial setup issues

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #8307
    Avataralreuben
    Participant

    Hi, I am a brand new user to Rapid SCADA, but not new to scada or modbus and the like. I am following a tutorial at http://rapidscada.net/doc/content/latest/en/use-cases/modbus-protocol.html but have very little luck in getting RS to pull data from my modbus device.

    I am hitting a wall; in the communication line I have created, the Line Log states:

    2021-02-21 14:51:45 Initialize communication line 4 “Email”
    2021-02-21 14:51:45 Start communication line 4 “Email”
    Loading address book
    2021-02-21 14:51:45 Error executing actions of Device 41 “Email sender” on communication line start: Error loading device settings:
    Length of the data to decrypt is invalid.

    This seems peculiar to me since I have nothing configured for email in any way.

    And going to the device, it says “File not found.”

    Help!

    • This topic was modified 1 month, 2 weeks ago by MikhailMikhail.
    #8310
    MikhailMikhail
    Moderator

    Hi,

    2021-02-21 14:51:45 Error executing actions of Device 41 “Email sender” on communication line start: Error loading device settings:

    This issue is not related to Modbus, but to the email sending driver.

    To fix:
    1. Download the driver update
    2. Configure email sending.

    In case of errors, post screenshot links to this topic.

Viewing 2 posts - 1 through 2 (of 2 total)