Hi, Im extracting data from a Power Meter through modbus. Scada is giving me Device error of GATEWAY PATH UNAVAILABLE. Ive tried extracting from the meter to a PLC, it was fine, read all the data. But for he actual application, I wont be needing the PLC . Thanks for the assistance in advance.
2022-06-07 14:51:18 Communication session with the Device 2 “Metro 2.0”, type: KpModbus, address: 1, call number: 192.168.1.3
Request element group
Send (12): 00 CD 00 00 00 06 01 03 0B CB 00 22
Receive (7/7): 00 CD 00 00 00 03 01
Receive (2/2): 83 0A
Device error: [0A] GATEWAY PATH UNAVAILABLE!
Request element group
Send (12): 00 CE 00 00 00 06 01 03 0B CB 00 22
Receive (7/7): 00 CE 00 00 00 03 01
Receive (2/2): 83 0A
Device error: [0A] GATEWAY PATH UNAVAILABLE!
Request element group
Send (12): 00 CF 00 00 00 06 01 03 0B CB 00 22
Receive (7/7): 00 CF 00 00 00 03 01
Receive (2/2): 83 0A
Device error: [0A] GATEWAY PATH UNAVAILABLE!
-