Viewing 15 posts - 6,211 through 6,225 (of 6,265 total)
  • in reply to: Any questions about Rapid SCADA and Raspberry Pi #219
    Dear Tom,
    I think Rapid SCADA perfectly fits your purposes. Of course you can use it.
    Rapid SCADA has low hardware requirements, full features and stable.
    Talking about possible problems, we have no enough statistics about working on Raspberry Pi because the appropriate version of the software was recently created.
    The best way is to start using Rapid SCADA on Raspberry and interact with me in this forum to discuss and solve issues.
    Thanks!
    in reply to: Configuration Error #217
    Most likely you need to choose IIS application pool that uses .NET 4.
    in reply to: Any questions about Rapid SCADA and Raspberry Pi #215
    Download binaries here.
    in reply to: Modbus RTU through TCP #212
    In the case of using Modbus RTU you need to create virtual serial port. The most of converters including Moxa supports creating virtual serial ports.
    Probably, Moxa converts Modbus RTU to Modbus TCP and the data exchange is correct as you show in the first sample, so you don’t need RTU.
    • This reply was modified 10 years, 12 months ago by Mikhail.
    in reply to: Communication delay with server #202
    1 and 2 seconds have to work. Try restarting IIS or PC.
    Does it work now?
    in reply to: Modbus RTU through RS485 #200
    Auto create channels feature doesn’t work for Modbus, unfortunately. The reason is that Modbus devices can contain different set of tags. You need to create channels manually. Use existing channels as templates. It is possible to clone them.
    12 should be entered in Address field of Devices table using SCADA-Administrator.
    40832 should be entered in the device template using SCADA-Communicator as described in the article.
    in reply to: Modbus RTU through RS485 #197
    Each energy meter is a device (a one row in the appropriate table of DB).
    Address column should contain a Modbus address (or ID) of a device.
    Call number is filled by IP address for Modbus TCP or left empty for Modbus RTU.
    in reply to: Modbus RTU through RS485 #195
    Object is a logical entity. For instance, a building or a house. Yes, it helps grouping of data and doesn’t affect communication with devices.
    A one object is enough for test purposes.
    in reply to: Modbus RTU through RS485 #193
    Dear Joel,
    Step by step instructions are described in this article. If some details are not clear, ask about the particulars in the topic.
    in reply to: Communication delay with server #189
    I think that using more powerfull hardware will not solve the problem. Any application has to do a delays those allow other applications operating.
    Did you set 50 ms delay into Request Sequence?
    What protocols are used by your devices? May be it is better to develop native drivers instead of OPC?
    in reply to: Communication delay with server #187
    Please check load of your CPU. Probably, setting 50 ms delay in Request Sequence tab is a good idea.
    Data refresh frequency that equals 0 works within schemes but does not work within table views.
    in reply to: Communication delay with server #185
    Great! Could you share how did you solve the issue?
    SCADA-Web interacts with SCADA-Server, not SCADA-Communicator.
    The default SCADA-Web data refresh frequency is 5 seconds. It is set in SCADA-Web Configurator. The minimum value is 1 second. So you can change the refresh rate.
    in reply to: Communication delay with server #183
    Firstly let’s realize a delay in SCADA-Communicator.
    Then I’ll describe other kinds of possible delays, OK?
    in reply to: Communication delay with server #182
    OPC Config
    in reply to: Communication delay with server #178
    Also try setting Update rate field for a data group in Device configration form that appears by clicking Properties item of device popup menu in Communicator.