  • in reply to: Hysteresis on input channel… #4294
    In this case, you do not need a hysteresis and just a timer with a delay off. TOF with time of 20 seconds.
    int[] TofNum = new int[1];
    long[] TofST = new long[1];
    bool[] TofFlag = new bool[1];
    public double Tof(double TofIn, double TofPT)
    long ET = 0L;
    long tof_pt = Convert.ToInt64(TofPT);
    bool q = Val(CnlNum) > 0;
    bool tof_in = TofIn > 0;
    int res = Array.IndexOf(TofNum, CnlNum);
    if (res == -1)
    res = TofNum.Length;
    Array.Resize(ref TofNum,  res+1);
    Array.Resize(ref TofST,   res+1);
    Array.Resize(ref TofFlag, res+1);
    TofNum[res] = CnlNum;
    if (tof_in)
    q = true;
    TofFlag[res] = true;
    TofST[res] = 0L;
    ET = 0L;
    else
    if (TofFlag[res])
    TofFlag[res] = false;
    TofST[res] = Ticks();
    ET = 0L;
     else
       if (q) ET = Ticks() - TofST[res];
     if (ET >= tof_pt) q = false;
    return Convert.ToDouble(q);
    Add in the Formula of the Administrator
    Configure the calculated channel formula – Tof(controlled channel, 20000)
    in reply to: AB driver integration for micrologix and micro800 series #4180
    C# can call functions of libraries written in C++ like. Not sure, but if I’m not mistaken, it is achieved using DllImport
    in reply to: Display and Set the String Value for tag #4113
    You use a standard command, and it takes numeric values. Probably it is necessary to use a binary command and convert the string representation to hex with a formula ?Maybe that’s the reason.
    in reply to: Scada development #4100
    You can, that’s how I wrote the driver to work with GPIO on Raspberry
    in reply to: ScadaSchemeEditor – Button use #4086
    in WEB Main menu-Configuration-Require password when sending command
    in reply to: ScadaSchemeEditor – Button use #4081
    I do not know what you have for the relay fee, I bought Chinese with Modbus in the documentation which was specified as on and off.
    256 – off, 512 – on, 768 – toggle
    I always gave the command 1 and multiplied by 768 and the relay changed its state. In other boards can be on different. Therefore, I try not to buy boards, which do not have a description, and then here on the forum there was an example when the Chinese mixed up the sequence of bytes of the checksum in Modbus
    in reply to: ScadaSchemeEditor – Button use #4074
    Command values
    Or you can use the standard command buttons from this database
    Sometimes the device should be fed not 0 or 1 but for example 256 or 512, then using the values for commands 1 and 2 additionally in the output channel multiply by 256 using the formula Cmd*256
    • This reply was modified 7 years, 8 months ago by manjey73.
    in reply to: ScadaSchemeEditor – Button use #4073
    example in the formula base: NOT
    public double NOT(double val)
        bool boolVal = val > 0;
        return Convert.ToDouble(!boolVal);
    In the output channel, write NOT (Cmd) and your command on the button will be changed to the opposite. Works only with 0 or 1 that actually follows from the name of the formula.
    It is not quite clear what you want to do with the separation of the buttons ?
    in reply to: Siemens Logo! Modbus #3965
    In response, the device says that it has included the network variable NI1, so most likely at the program level it is not included.
    in reply to: Siemens Logo! Modbus #3963
    c Q2 you have no problem because it is not yet tied to the program. Q1 may not be enabled due to overwriting in the program. Now there is no Logo at hand! Soft Comfort to understand.
    As for the lack of response to the NI1 input, a possible problem is that the Communicator sends to the double device,and the input user variables you have are word. The formula for rearranging the bytes before sending the command.
    • This reply was modified 7 years, 9 months ago by manjey73.
    in reply to: Siemens Logo! Modbus #3961
    You have a table of registers from the manufacturer Logo! ?
    Status of inputs and outputs.
    Plus, the other registers you create yourself in the program Logo! and there should be a register card after its programming.
    in reply to: log storage location #3948
    install_with_xsp.txt or 13 file install_with_apache.txt
    10. In case of using SD card, protect it by moving frequently used folders to RAM.
    Skip this step if you use a regular HDD.
    Add the lines below to /etc/fstab
    tmpfs /tmp tmpfs defaults,noatime,size=50m 0 0
    tmpfs /var/log tmpfs defaults,noatime,size=50m 0 0
    tmpfs /opt/scada/ScadaComm/Log tmpfs defaults,noatime,size=100m 0 0
    tmpfs /opt/scada/ScadaServer/Log tmpfs defaults,noatime,size=10m 0 0
    tmpfs /opt/scada/ScadaWeb/log tmpfs defaults,noatime,size=10m 0 0
    tmpfs /opt/scada/ArchiveDAT/Cur tmpfs defaults,noatime,size=10m 0 0
    in reply to: log storage location #3940
    Mount the disk to fstab and specify the path to save the databases to the appropriate folder.
    in reply to: General Configuration Sequence #3883
    You don’t have a system tray that shows the clock, keyboard layout, network status, mixer status, battery, and so on.
    You only have the Task Bar work area
    • This reply was modified 7 years, 10 months ago by manjey73.
    in reply to: How to uninstall SCADA #3847
    Run Setup again, there will be a choice of installation or removal.