MikhailModeratorThe OPC UA server that is built in Communicator cannot send commands to the application. You should look for another way of sending commands to Rapid SCADA. May be, via a database or 3rd party OPC server.
Do you mean to include .NET inside Rapid SCADA executables?
MikhailModeratorCreate 2 channels of the Calculated/Output type in the Channels table.
Specify their numbers in the Limits table in a limit row.
Display the created channels in a table view.
Then provide screenshots.
MikhailModeratorCould you provide screenshots of the settings and error?
MikhailModerator🙂
I’m not sure that it can work on Windows ARM.
If the Rapid SCADA services work, check log files ScadaServer.log, ScadaComm.log and ScadaWeb.log
MikhailModeratorIn this case, create 2 extra channels, max and min. Set them as limits of the 1st channel (see this page). To display them on a chart, you need to select them manually or display chart as a view with predefined channels.
MikhailModeratorDo you mean that you need to restart a line by another OPC UA client?
If so, you need a channel that can be changed by the client, and use Automatic Control Module to send a command depending on that channel.
Channel formula example,
Cnl <= 10 ? Cnl : 0
Condition ? expression1 : expression2
MikhailModeratorCurrent driver version supports number values. We will support 4 char strings in the next driver version.
You have to fill the tags in the device properties. One tag per line
MikhailModerator> I just want to know how many Y axes can be used at most
There is no software limit. If you create too many axes, they will appear ugly, I suppose.
MikhailModeratorCreate a channel of the Output type and set Tag Code to the above.
In version 6 you can send a command to restart a line.
Supported commands are here.
Command value is a line number to restart.
MikhailModeratorYes, this timeout also affects how long it waits for service command execution.