oley
Viewing 15 posts - 76 through 90 (of 93 total)
  • in reply to: Reading event log from modbus device #16697
    oley
    This is a bit complicated, so I’ll try to explain again.
    I read 0x0501 and can get:
    – 0, that is, no new event has occurred since the last reading of 0x0501
    – a value greater than 0, such as 5, and then I have to read addresses 0x1000 to 0x1005 to get 5 events
    in reply to: Reading event log from modbus device #16696
    oley
    it would be good to generate SCADA events based on those events, so I have it in standard event list.
    in reply to: Reading event log from modbus device #16689
    oley
    I have got some information from the manufacturer of the device.
    Address 0x0501 contains count of the new events since last reading.
    Address 0x0502 contains total count of the events, max 1024.
    Address range 0x1000-0x13FF contains events from the most recent and it is locked until the register 0x0501 or 0x0502 is read again.
    What if I create group of channels from 0x1000 to 0x13FF and every channel will have formula:
    channel 0x1000 -> if (channel0x0501 > 0 and channel0x0502 > 0)
    channel 0x1001 -> if (channel0x0501 > 1 and channel0x0502 > 1)
    and so on?
    If I activate the events for each channel, so they will appear in the event log.
    Is this possible?
    Best regards
    in reply to: Swapping command values #16688
    oley
    thank you. The custom enumeration works properly.
    Best regards
    in reply to: Reading event log from modbus device #16576
    oley
    I am in contact with the manufacturer of the device, because the documentation does not specify this.
    Is the code of this S2000-PP driver available for review?
    in reply to: Reading event log from modbus device #16569
    oley
    I’m familiar with .NET so driver that decomposes events is a good option.
    Should it be a class derived from DevModbusLogic?
    in reply to: Reading event log from modbus device #16567
    oley
    During SCADA running, I can polling the counter for new events (separate register 0x0500) and read as many as occurred.
    After a restart, I would have to read all the events that I did not save in the database to archive the full history.
    in reply to: Reading event log from modbus device #16565
    oley
    I’m not sure if I can make it with Automatic Control Module.
    This device has a register range for events, which is a circular buffer.
    One event is written in 8 registers:
    0 Event code
    1 Value: Lo(Int1), Hi(Int2)
    2,3 Value float
    4 Lo(month), Hi(end of year)
    5 Lo(hour), Hi(day)
    6 Lo(second), Hi(minute)
    7 milliseconds
    The last event is under 0x1000, the pass under 0x1008, and so on.
    I would like to save all events in the database and present them in a view already from the database. I think this is the easiest way. The complicated part is reading from the device and storing them in the database.
    in reply to: Reading event log from modbus device #16559
    oley
    Thank you for your advice.
    I will check if reading from one address is enough.
    I will also try the Automatic Control Module and come back with any further questions.
    in reply to: Reacting on external data #16546
    oley
    Thanks!
    in reply to: Add calculated channels to OPC UA Server #16480
    oley
    @odobrev
    Got it!
    It was the LAN port. I have used the second one for the connection.
    After replacement of the port I can connect.
    Thank you for your help!
    in reply to: Add calculated channels to OPC UA Server #16478
    oley
    @odobrev
    Thanks again!
    Unfortunately I can not establish the connection with an error in line log: “No connection could be made because the target machine actively refused it”.
    Probably some network setting are wrong. I am doing it on fresh Windows 11 VM, firewall is completely disabled. Adresses are ok, I can ping and log in via browser into logger interface.
    I tried Modbus TCP settings with Link setting Limited and IP address as you mentioned also with unlimited access.
    What are your Modbus TCP settings on the logger?
    Address mode Logical/communication address
    Logger address
    Fast scheduling
    Do you use LAN or WAN port on the logger?
    in reply to: Add calculated channels to OPC UA Server #16474
    oley
    @odobrev
    No problem, thanks!
    I’ll try it out right away!
    in reply to: Add calculated channels to OPC UA Server #16463
    oley
    sorry, the question was addresserd to @odobrev.
    He said, he will provide some example config to Huawei device which I try to connect via Modbus TCP.
    in reply to: Add calculated channels to OPC UA Server #16459
    oley
    Are you already back from vacation and could you help with MODBUS TCP configuration. I’ve run SmartLogger and enabled ModBus, but I’m having trouble connecting and thought I’d wait for a sample configuration.
    Best regards