Hi
I am trying to connect Rapid scada wit modbus simulator modsim
Every thing goes gine
SCADAComm recives data from simulator that i can see in communication line log
But the value are not displaying in web page is just displaying — (dash)
how to make value display??
Hi,
If you click a device node in SCADA-Communicator, there should be your channel numbers in the grid in “Device Data” page. Are they displayed?
If not, probably you need to open SCADA-Administrator, click “Pass to SCADA-Server” toolbar button and restart SCADA-Server and SCADA-Communicator services.
I also clicked the button “Pass to SCADA-Server”
and restart the SCADA-sever and SCADA-commuicatr servies
but still channel numbers are not in the grid
In Device Data page value grid changes if change value in modbus RTU simulator
Most likely, communication line number and device number in the configuration database aren’t matched communication line number and device number in SCADA-Communicator.