The averaging column in SCADA Admin input channels

Forum Home Forums Understanding the Software The averaging column in SCADA Admin input channels

Viewing 4 posts - 1 through 4 (of 4 total)
  • Author
    Posts
  • #2485
    MohanadOdema
    Participant

    Hi,

    I want to make sure that I understand the averaging column’s function correctly. Does it take the average of (the newly updated reading with a number of previous readings) ? If so, is there a way to control the number of points to be taken in the averaging computation ?

    Thanks in advance.

    #2489
    Mikhail
    Moderator

    Hi,
    For minute data:
    It summarizes the values which were received during the minute and divide the sum by the number of values.

    For hourly data:
    The same, but values are summarized during the hour.

    You can calculate number of points if create a formula that increases a counter each time when it is calculated by SCADA.

    #2509
    MohanadOdema
    Participant

    So if I have understood correctly, this means that if I have an input channel and I want the average per hour to be displayed as in hourly data, I should do the following:

    1- change the channel type to hourly real
    2- mark averaging column

    Correct?

    #2512
    Mikhail
    Moderator

    1. Not “hourly real”, but “real”.
    2. Yes.

Viewing 4 posts - 1 through 4 (of 4 total)