Forum Home › Forums › Communicating with Devices › Modbus › disable Máximum failed session count en 4.5
- This topic has 5 replies, 2 voices, and was last updated 7 years, 10 months ago by
Mikhail.
-
AuthorPosts
-
November 6, 2015 at 4:03 am #663
jeeslo
ParticipantHi!
I made the upgrade from version 4.4 to version 4.5 with this last problem that I have with the Scada communicator is Modbus, is that with this new parameter “Device request retries count on error” that varies from 1-100 when the network is stuffy or for any other reason the communicator has many mistakes me for the process completely, with version 4.4 I had no problem. As I can disable “Device request retries count on error” comm. session errors in the Line?I want the line active continue to work with or without network errors
November 6, 2015 at 7:54 am #670Mikhail
ModeratorHi,
Please post here a part of communication line log. I recommend to leave Device request retries count on error unmodified and equal to 3.November 19, 2015 at 5:08 pm #729jeeslo
ParticipantHi Mikhail!!!
This is what happens when such (Requests (total / errors): 142/3) when it reaches the number 3, the communicator device is disconnected. To resolve I have to restart the whole Scada-Comunicator ver.4.5.0.2
I’ve tried changing “Device request parameter count retries on error” to the maximum that is always reaching 99 error number for all communication.With version 4.4 everything worked perfectly.
File Line001 LOG:
2015-11-19 10:30:59 Establish a TCP connection with 172.16.182.24:502
Error establishing TCP connection: Once the socket has been disconnected, you can only reconnect again asynchronously, and only to a different EndPoint. BeginConnect must be called on a thread that won’t exit until the operation has been completed.2015-11-19 10:30:59 Unable to communicate with the device because connection is not established
2015-11-19 10:30:59 Establish a TCP connection with 172.16.190.111:502
Error establishing TCP connection: Once the socket has been disconnected, you can only reconnect again asynchronously, and only to a different EndPoint. BeginConnect must be called on a thread that won’t exit until the operation has been completed.2015-11-19 10:30:59 Unable to communicate with the device because connection is not established
2015-11-19 10:30:59 Establish a TCP connection with 172.16.182.26:502
Error establishing TCP connection: Once the socket has been disconnected, you can only reconnect again asynchronously, and only to a different EndPoint. BeginConnect must be called on a thread that won’t exit until the operation has been completed.2015-11-19 10:30:59 Unable to communicate with the device because connection is not established
2015-11-19 10:30:59 Establish a TCP connection with 172.16.182.151:502
Error establishing TCP connection: Once the socket has been disconnected, you can only reconnect again asynchronously, and only to a differScada-Comunicator Comunicator Line Log:
2015-11-19 10:35:49 Establish a TCP connection with 172.16.182.24:502
Attempt to establish TCP connection can not be earlier than 5 seconds after the previous.November 19, 2015 at 10:53 pm #734Mikhail
ModeratorYou have found a major bug. Thanks!
I’ve sent you a fix. Please try it and post a result here.Do not forget to return Device request retries count on error back to 3.
November 20, 2015 at 6:08 pm #736jeeslo
ParticipantMikhail Hello!
I have good news!! I tried the .dll received and worked perfectly.
I thank you very much for your help.
Good day!!
November 20, 2015 at 6:40 pm #737Mikhail
ModeratorHi,
Good news 🙂
Thank you for your help in finding the cause.
I’ll include the fix in the distributive within a few days. -