Modbus TCP Device ID

Forum Home Forums Communicating with Devices Modbus Modbus TCP Device ID

  • This topic has 3 replies, 4 voices, and was last updated 8 months ago by JW.
Viewing 4 posts - 1 through 4 (of 4 total)
  • Author
    Posts
  • #15788
    fischerp
    Participant

    Hello,
    I am trying to connect a Modbus RTU device that is connected to a TCP device as a sub-device.

    Using the usual Modbus test tools, I can find the values by specifying the ID used in the internal communication between the two (TCP and RTU) devices as the device ID.
    Device ID Radzio
    In Rapid Scada, I have now created a new device with the IP address of the “main device” and the numerical address corresponding to the device ID.
    Device ID Rapid
    As I understand it, this should be the correct procedure? I get values, but not the expected ones.
    What am I doing wrong?

    • This topic was modified 8 months ago by fischerp.
    #15798
    Mikhail
    Moderator

    Hello,
    Your description is correct.
    I suggest to compare Modbus packets sent by Rapid SCADA and the other software.

    #15826
    manjey73
    Participant

    Addressing – start with 0 or 1
    It is possible to specify byte permutation for 4 and 8 byte data

    #15827
    JW
    Participant

    The Device ID (Slave ID) looks correct, since you can connect and get data.

    The issue with incorrect data you encountered could be the holding register address instead of the Device ID.

    On your 1st screenshot, the address test software is 0 based, and use 40000 data block as holdings register.

    While Rapid SCADA administrator is 1 based, and use 03h function code as holding register.

    40 holding registers from 40080 on your test app equals 40 registers from 81 of 03h function on scada settings ui.