June 28, 2023 at 5:53 pm #12898
scr910
ParticipantI have successfully implemented basic table and scheme views for a locally run project using Modbus values communicated via a direct ethernet connection and via a Wi-Fi access point on my Modbus Gateway module which is connected to my PLC. My goal is to connect this Modbus Gateway to a Wi-Fi network that my localhost (my computer) running the project is also connected to and communicate via this Wi-Fi network.
I have connected the Modbus Gateway to the network and repeatedly pinged the Modbus Gateway from my computer, establishing that I can at least ping via the Wi-Fi network. However, the Modbus communication is not working. Assuming I have configured the Modbus Gateway properly (which I am not totally sure of but I think everything is okay), is there anything I can change in my RapidScada project that can solve this communication issue?
I know my call number/host name for the device is correct.
The communication line parameters are as follows:
TCP Client
Host =
TcpPort = 502
ReconnectAfter = 5
StayConnected = True
Behavior = Master
ConnMode = IndividualThe Modbus Gateway page states: “Your ACE-PLC is available via Modbus-TCP at the new IP address and Ethernet port 502”
Any advice at all is appreciated, networking is not my strong suit as you might guess!
June 28, 2023 at 5:57 pm #12899Mikhail
ModeratorHello,
Could you post a part of communication line log from Communicator?June 28, 2023 at 6:03 pm #12903scr910
ParticipantHere it is:
2023-06-28 13:01:53 Unable to communicate with Device 1 “Velocio_PLC” because connection is not established
2023-06-28 13:01:53 Attempt to establish TCP connection can not be earlier than 5 seconds after the previous.
2023-06-28 13:01:53 Unable to communicate with Device 1 “Velocio_PLC” because connection is not established
2023-06-28 13:01:53 Attempt to establish TCP connection can not be earlier than 5 seconds after the previous.
2023-06-28 13:01:53 Unable to communicate with Device 1 “Velocio_PLC” because connection is not established
2023-06-28 13:01:53 Attempt to establish TCP connection can not be earlier than 5 seconds after the previous.
2023-06-28 13:01:53 Unable to communicate with Device 1 “Velocio_PLC” because connection is not established
2023-06-28 13:01:53 Attempt to establish TCP connection can not be earlier than 5 seconds after the previous.
2023-06-28 13:01:53 Unable to communicate with Device 1 “Velocio_PLC” because connection is not established
2023-06-28 13:01:54 Establish a TCP connection with 192.168.8.1:502
It says it is looking for the IP which I use for ethernet/direct Wi-Fi access point connection. This is interesting, I have not looked at this page before. Thank you!
June 28, 2023 at 6:06 pm #12904scr910
ParticipantWhen I restart:
——————————————————————————–
2023-06-28 13:05:46 Initialize communication line 1 “Modbus”
2023-06-28 13:05:46 Load device template from file KpModbus_FTEG70_Diagnostics.xml
2023-06-28 13:05:46 Start communication line 1 “Modbus”2023-06-28 13:05:47 Establish a TCP connection with 192.168.8.1:502
Error establishing TCP connection: A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond 192.168.8.1:5022023-06-28 13:06:08 Unable to communicate with Device 1 “Velocio_PLC” because connection is not established
2023-06-28 13:06:08 Attempt to establish TCP connection can not be earlier than 5 seconds after the previous.
2023-06-28 13:06:08 Unable to communicate with Device 1 “Velocio_PLC” because connection is not established
June 28, 2023 at 7:59 pm #12905scr910
ParticipantI created a new communication line and it worked, so I am now communicating via the Wi-Fi network. Thanks again for pointing me towards the log Mikhail!
June 29, 2023 at 3:49 am #12908Mikhail
ModeratorI’m glad that now it works.
Thank you for update.June 29, 2023 at 8:21 pm #12915TDE
ParticipantHi,
I’m a new user of Rapid Scada and I’m still curious about this interesting software.
I have implemented a communication link with the PLC to track the status of the machine via a Modbus TCP connection.
================================================
The communication line parameters are as follows:
TCP Client
Host =
TcpPort = 502
ReconnectAfter = 5
StayConnected = True
Behavior = Master
ConnMode = Individual
==========================================
When I tried to send values from the PLC to see how the information is coded. The output was as follows:
The first element group includes 14 elements. I force the values of the first octet = 16 and second octet = 2 inside the PLC holding registers and I can see that FF and 02 refer to this change.My question is:
1- can you please explain to me why it is coded as FF and 02? why not as F and 2.
2- What does it mean, Send (12), Receive (7/7), and Receive (54/54)
3- Why the first two values (03 34) does not change? do they have a relation with communication protocol or what?==============================================================================
2023-06-29 13:54:06 Session with the device [1] modbus_device
Request element group “HMI”
Send (12): 85 DD 00 00 00 06 00 03 00 00 00 1A
Receive (7/7): 85 DD 00 00 00 37 00
Receive (54/54): 03 34 FF 02 00 00 00 00 01 80 00 05 00 00 00 00 00 00 00 00 00 00 00 00 00 00 40 0E E1 A0 E0 05 E1 A0 50 04 E5 1A 60 51 E3 A0 06 95 E0 05 BD 98 E5 9F 60 05 E0 8B
OK
==============================================================================Thank you for your understanding.
June 30, 2023 at 4:22 am #12917Mikhail
ModeratorHi,
1 and 3. Decode the packets using https://rapidscada.net/modbus
When you copy data to the form, split the received data.2. Send and Receive are the operations performed by the driver.
7/7 means that 7 bytes read and 7 bytes required. -