Modbus communication error
Forum Home › Forums › Communicating with Devices › Modbus › Modbus communication error
  • #5779
    dineshkumargowd
    Dear Mikhail,
    I am trying to communicate with Modbus Data acquisition module whose address is 1, baud rate is 9600, parity = No, stop bit = 1. I have assigned holding registers in modbus template. When i am starting the communicator i am receiving the communication error. Kindly help in this regard.
    Initially i was using another version of Rapidscada, i was able to read those registers with the old version. But i am unable to read them from the new version of 5.7.
    Following is the communication log for your reference
    2019-08-01 18:29:28 Communication session with the Device 61 “E830_DAQ”, type: ScadaCommCommon, address: 1
    Request element group
    Send (8): 01 03 00 01 00 08 15 CC
    Receive (0/5):
    Communication error!
    Receive (0/5):
    Receive (0/5):
    #5780
    Working with Modbus devices was not changed in Rapid SCADA 5.7. From the log we can see that the device doesn’t respond. You should check serial connection.
    #5782
    dineshkumargowd
    Dear Mikhail,
    It worked Now.
    Device was not responded, since i have assigned the Holding registers(one register – 02 bytes) as Unsigned(16) initially. Later on changing them all to Signed(16), it worked well.
    Serial connection was good, since it worked with other Modbus Master software.
    Thanks for your immediate response.
    #5785
    Thank you for the info.