Modbus Byte order for PM2100 Series Meter
Forum Home Forums Communicating with Devices Modbus Modbus Byte order for PM2100 Series Meter
Viewing 5 posts - 1 through 5 (of 5 total)
  • #3678
    dineshkumargowd
    Dear Sir,
    I am trying to read holding register from Schneider Easylogic PM2100 series power meter, but unable to read it. I am getting following errors
    1. Device 102 “11KV Swst” : error
    2018-05-08 09:48:03 Communication session with the Device 102 “11KV Swst”, type: KpModbus, address: 10
    Request element group “Voltage group”
    Send (8): 0A 03 0B CA 00 02 E7 6A
    Receive (5/5): 0A 83 03 70 F3
    Device error: [03] ILLEGAL DATA VALUE!
    I have tried with multiple byte order like ab cd, dc ba, ba dc, cd ab but in every sequency same errors were occurring. Kindly do needful ASAP
    #3679
    manjey73
    A link to the list of registers PM2100. Perhaps when prompted in RapidScada need to specify the address of the register + 1
    #3680
    manjey73
    https://www.schneider-electric.ru/ru/faqs/FA334611/
    Read the document carefully. The voltage starts from the register 3020, it may be necessary to add to the registers +1, that is, to start with 3021
    Since there is no register between 3018 and 3020, you get an error from the device
    • This reply was modified 8 years, 4 months ago by manjey73.
    #3682
    dineshkumargowd
    Dear Manjey73,
    Yes i have started the addres from 3020 to 3021 and it worked. thanks for your valuable reply.
    #3684
    In addition, you can choose addressing (zero based or 1 based) in the template settings.