    Hi Mikhail

    There is a plan add other function codes to KpModbus.dll?
    Specially 16(10hex) which is frequently used in modbus devices.
    Will be nice even it will be available in comercial(paid) version

    For that I checked few trial version of OPC servers just for this funcjonality but no one works soo easy as KpModbus plugin.

    #2108
    Mikhail
    Moderator

    Hi,
    Function 0x10 already supported. The driver KpModbus.dll uses 0x10 function if you tick Multiple checkbox for a command.

    #2109
    MarCus0
    Participant

    Hi
    Thanks I will check.
    Thanks for a promptly answer.
    Marek

    #2110
    MarCus0
    Participant

    KpModbus - command

    Hi

    See screenschot.
    Under dropbox is marked tick multiple.
    I good understand that for single coil(0x) will be 05(0x05), multiple will be 15(0x0F) and for (4x)holding register 06(0x06)-for single and 16(0x10)-for multiple write? I’m not at home just have some test instalation at front.

    Regards

    #2111
    Mikhail
    Moderator

    Hi Marek,

    That’s right. You can check here.
    But the best way to check is watching communication log in Communicator.

Viewing 5 posts - 1 through 5 (of 5 total)