issue to get real value through modbus tcp
Forum Home › Forums › Communicating with Devices › Modbus › issue to get real value through modbus tcp
  • #9448
    modivir
    hi,
    I have communicate rapid scada with schneider PLC through modbus tcp. but I am not able to see actual value(real value) in rapid scada. I have attached a scheneider PLC image, rapid scada images.
    https://drive.google.com/drive/folders/1g-J5cFHWyIK63gAJzXrydK5Myyuo7gXC?usp=sharing
    • This topic was modified 5 years, 2 months ago by Mikhail.
    #9458
    Could you make a screenshot of the Modbus template, device data page and copy request and response as text?
    #9468
    modivir
    YES, ATTACHED IN ABOVE LINK
    #9471
    The above link contains none of the requested info.
    #9515
    BriggTrim
    Hi….At the point when you say the CPU sends information through Modbus/TCP to SCADA that would deciphered as Modbus ace/customer composing information to the worker/slave SCADA framework, rather than the SCADA framework ace/customer perusing the information from a worker/slave PLC.
    About close to 100% of genuine, gliding point information in Modbus is 32 bit IEEE 754 drifting point (FP) values, containing two 16 bit Modbus enrolls in IEEE design. The other 1% is 64 bit skimming point information. At the point when you notice, “two words” I am speculating that you mean two 16 bit Modbus registers that will hold the 32 bit FP information.