April 3, 2024 at 2:49 pm #14332
sperate
ParticipantHi,
I’m having this message while trying to add an OPC remote server to rapid SCADA:
Error filling server list : CoCreateInstanceEx: RPC Server is not available
Something’s missing ?
April 3, 2024 at 3:53 pm #14333sperate
ParticipantIs ther some place in the configuration to specify the TCP port used by the OPC DA server ? Does the OPC Classic driver need this kind of information ?
Regards
April 4, 2024 at 11:33 am #14336Mikhail
ModeratorHi,
May be you need to install OPC Core Components (available on our website).
Also, you should configure access rights in DCOM settings, which can work unpredictable.
OPC DA does not need to specify TCP port.Consider installing the Communicator service on the same machine as OPC server. Communicator can send data to SCADA-Server remotely. And configuration may be simplified.
April 8, 2024 at 4:17 pm #14368sperate
ParticipantI don’t have rights/acces to the machine on witch the OPC server is installed.
OPC Core Components is installed on the client side (RapidSCADA) => OK
Also, you should configure access rights in DCOM settings, which can work unpredictable. On server or client side ?
Many thanks !
April 9, 2024 at 9:55 am #14372JurasskPark
ParticipantOn server or client side ?
On the server side.
You must create a Windows account there, which will be identical in login and password. And give her rights to the computer, DCOM and OPC server.April 9, 2024 at 11:22 am #14373Mikhail
ModeratorYou can use this simple utility for testing. Also try 3rd party OPC clients, such as Matrikon OPC explorer and Prosys.
April 11, 2024 at 6:27 am #14377sperate
ParticipantMany thanks for your answers and the browseOPC software !
I was already using MatrikonOPC but Matrikon is asking for the server name in order to try to connect. As I don’t have the credentials and I am not allowed to access to the server, the administrator will provide me a sort of tunneler that will deal with all this DCOM/Windows credentials stuff and create a local instance of the OPC Server on the Client side (where RapidSCADA is installed).April 11, 2024 at 10:35 am #14382Mikhail
ModeratorDid you manage to connect?
April 11, 2024 at 4:47 pm #14384sperate
ParticipantNot yet as the server is not available right now but it should be ok with the tunneller.
I can see now the local instance of the OPC server created by the tunneler but I can’t connect to it to add tags because the server is not reachable.I’ll keep you up to date.
-
This reply was modified 1 year, 4 months ago by
sperate.
April 15, 2024 at 8:46 am #14393sperate
ParticipantConnection OK !!!
Very hard to deal with those OPC Classic servers
April 15, 2024 at 9:37 am #14399Mikhail
Moderator> Connection OK !!!
Nice!> Very hard to deal with those OPC Classic servers
That’s true. -
This reply was modified 1 year, 4 months ago by
-
AuthorPosts